03-03-2006, 09:56 AM #1
R744 Supermarket Rack
Hi guys, haven't been to RE in a while, nice to see some of the same threads STILL going
Thought I might show some fotos of an R744 (Co2) rack running in a supermarket. Store load is split over 2 cascade systems (R744/R507). Each R744 rack has 2 comps for the LT load, liquid recirc is used for MT&HT loads. 2 x H/Xchs as cond for R744/R507 evap and a normal 4 comp rack as hi stage. Hi stage is water cooled, closed loop with Guntner hybrid coolers used.
LP on R744 runs around 1400 kpa (-28ish SST), vessel kept at 2400 kpa (-11ish SCT), R507 rack runs around -15 SST to keep vessel -10 to -11 SCT. Copper pipe used for all pipe runs except larger dia. rack piping, largest size is 5/8" on shopfloor.
Sorry fotos are pretty avg, only had a camera fone, will try to get better res. shots.
IMAGE_00062.jpg
IMAGE_00067.jpg
IMAGE_00071.jpg
IMAGE_00072.jpg
IMAGE_00076.jpg
-
03-03-2006, 10:59 AM #2
Re: R744 Supermarket Rack
good to se you back - was re-reading the au thread and I did wonder where you'd got
cheers
richard
-
04-03-2006, 12:05 AM #3
Re: R744 Supermarket Rack
Hi 750! How much R507 is in your system?
-
04-03-2006, 03:18 AM #4
Re: R744 Supermarket Rack
Thanks for posting the very interesting pictures. I for one would be very interested to find out more information about this system.
-
27-07-2006, 11:22 PM #5
Re: R744 Supermarket Rack
Hi 750,fficeffice" />
>>
Thanks for the interesting Co2 rack pix… and for sharing your nice “moustache” with us… just watch out for liquid flooding! ;o)>>
-
28-07-2006, 03:32 AM #6
Re: R744 Supermarket Rack
I wasn't allowed photos, but just got back from a CO2 secondary refrigerant startup in a Sam's Club. I noted that there was about 1,100 lbs of CO2 in the A rack, so I would expect the same in the other machine, more or less. At any rate, an exposure of leakage under $2,000.00.
They have a separate generator with a backup compressor to keep the pressures below 500 psig in the event of a power failure. My guess is the refrigerant charge is around 1,000 lbs of R404A.
I see much sense in using secondary refrigerants such as glycol and CO2, as we confine the piping, exposure, and voume of gasses that perhaps contribute to global warming.
Similar Threads
-
Maintenance of supermarket equipment
By ronsin1 in forum Supermarket RefrigerationReplies: 5Last Post: 03-05-2010, 03:41 AM -
Supermarket refrigeration training
By Deejey in forum Supermarket RefrigerationReplies: 5Last Post: 25-04-2006, 04:08 AM -
Maintaining Supermarket Refrigeration System
By Cofreth in forum Supermarket RefrigerationReplies: 17Last Post: 12-10-2005, 10:24 PM -
Servicing Supermarket Reach-in Freezers
By shogun7 in forum Supermarket RefrigerationReplies: 12Last Post: 30-04-2004, 12:05 AM -
Supermarket Refrigeration
By bersaga in forum Trouble ShootingReplies: 11Last Post: 01-12-2003, 03:40 PM