    R744 Supermarket Rack



    Hi guys, haven't been to RE in a while, nice to see some of the same threads STILL going
    Thought I might show some fotos of an R744 (Co2) rack running in a supermarket. Store load is split over 2 cascade systems (R744/R507). Each R744 rack has 2 comps for the LT load, liquid recirc is used for MT&HT loads. 2 x H/Xchs as cond for R744/R507 evap and a normal 4 comp rack as hi stage. Hi stage is water cooled, closed loop with Guntner hybrid coolers used.
    LP on R744 runs around 1400 kpa (-28ish SST), vessel kept at 2400 kpa (-11ish SCT), R507 rack runs around -15 SST to keep vessel -10 to -11 SCT. Copper pipe used for all pipe runs except larger dia. rack piping, largest size is 5/8" on shopfloor.
    Sorry fotos are pretty avg, only had a camera fone, will try to get better res. shots.

    IMAGE_00062.jpg

    IMAGE_00067.jpg

    IMAGE_00071.jpg

    IMAGE_00072.jpg

    IMAGE_00076.jpg



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: R744 Supermarket Rack

    good to se you back - was re-reading the au thread and I did wonder where you'd got

    cheers

    richard

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: R744 Supermarket Rack

    Hi 750! How much R507 is in your system?

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: R744 Supermarket Rack

    Thanks for posting the very interesting pictures. I for one would be very interested to find out more information about this system.

  5. #5
    globalcooling's Avatar
    globalcooling Guest

    Re: R744 Supermarket Rack

    Hi 750,fficeffice" />>>
    Thanks for the interesting Co2 rack pix… and for sharing your nice “moustache” with us… just watch out for liquid flooding! ;o)>>

  6. #6
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: R744 Supermarket Rack

    I wasn't allowed photos, but just got back from a CO2 secondary refrigerant startup in a Sam's Club. I noted that there was about 1,100 lbs of CO2 in the A rack, so I would expect the same in the other machine, more or less. At any rate, an exposure of leakage under $2,000.00.

    They have a separate generator with a backup compressor to keep the pressures below 500 psig in the event of a power failure. My guess is the refrigerant charge is around 1,000 lbs of R404A.

    I see much sense in using secondary refrigerants such as glycol and CO2, as we confine the piping, exposure, and voume of gasses that perhaps contribute to global warming.

Similar Threads

  1. Maintenance of supermarket equipment
    By ronsin1 in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 03-05-2010, 03:41 AM
  2. Supermarket refrigeration training
    By Deejey in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 25-04-2006, 04:08 AM
  3. Maintaining Supermarket Refrigeration System
    By Cofreth in forum Supermarket Refrigeration
    Replies: 17
    Last Post: 12-10-2005, 10:24 PM
  4. Servicing Supermarket Reach-in Freezers
    By shogun7 in forum Supermarket Refrigeration
    Replies: 12
    Last Post: 30-04-2004, 12:05 AM
  5. Supermarket Refrigeration
    By bersaga in forum Trouble Shooting
    Replies: 11
    Last Post: 01-12-2003, 03:40 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •