    Apr 2009
    Pergamino
    55
    5
    TRANE CHNN035 master valve oil
    hi for all, I have a problem with a Trane chiller RTAA070 that holds oil in the separator in one of the circuits. Can it be that the master valve not closing properly oil? In that case, you know how to access it?. Thank for you time. Best regards from Argentina
    Oct 2009
    merida mexico
    54
    282
    Re: TRANE CHNN035 master valve oil
    could you give me the complete model of the machine? and model of compressor?
    greetings from Mexico
    Apr 2009
    Pergamino
    55
    5
    RTAA070KXJ01A000B, and the compressor CHNN035TKD0N043A, thanks
    Oct 2009
    merida mexico
    54
    282
    RTAA machine does not have that capacity solenoid valve teacher.
    the three that has the compressor valves are below
    loading solenoid valve
    solenoid valve discharge
    load solenoid valve female lobe
    what is your problem with this machine in my profile if you like my email to this comment
    Apr 2009
    israel
    778
    if you mail me i will send you the manual.
    Oil System Operation
    Overview
    Oil that collects in the bottom of the oil
    separator is at condensing pressure
    during compressor operation;
    therefore, oil is constantly moving to
    lower pressure areas. Refer to
    Figure 43.
    As the oil leaves the separator, it passes
    through the air-cooled oil cooler at the
    top of the condensing coils. It then
    goes through the service valve and
    filter. At this point, some of the oil is
    used to control the slide valve
    movement in the compressor, via the
    load/unload solenoids. The remaining
    oil passes through the oil master
    solenoid valve and performs the
    functions of compressor bearing
    lubrication and compressor oil
    injection. If the compressor stops for
    any reason, the master solenoid valve
    closes, isolating the oil charge in the
    separator and oil cooler during “off”
    periods
    good luck
    Apr 2009
    Pergamino
    55
    5
    the problem is that the oil is not skeptical before its level in the separator. By the method of liquid viewer I can not oil level. In addition, the PLC shows "lubrication system failure". The machine has 12 years of use and never damage the refrigerant circuit. then, oil has never lost either.
    Goshen: I have the manual but does not clarify what the master valve oil.
    thanks.
    Apr 2009
    Pergamino
    55
    5
    According to the manual (Figure 22) the master oil valve is a pressure actuated valve and not a valve solenoid
    Apr 2009
    israel
    778
    Hii would check your oil filter !a diff presostat is probably feeling a big drop in pressure .change your filter or at least messure the pressure drop according to trane specs and take it from there!good luck
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    Quote Originally Posted by SUPERWILLY View Post
    thanks.
    What is the run time before it is going to trip. Have you checked oil difference between oil filter. From your post I understand that you can see the oil level in separator, and then is going to trip. Or do you mean that you cannot see the oil level in separator? As per the diagram oil line solenoid is not pressure actuates, it electrical solenoid valve.
    Apr 2009
    Pergamino
    55
    5
    the oil level is lower than required by trane (<5 "), the differential pressure is 1 psi, the oil valve is not electrical. Only has three solenoid valves, are the control of loading and unloading of compressor.
    Oct 2009
    merida mexico
    54
    282
    verifies that the temperature sensors are well
    saturated condenser temperature sensor
    oil temperature sensor
    diff -4 ° f lubrication failure
Tags for this Thread