Results 1 to 11 of 11
Thread: R417a
    Aug 2002
    Lancashire
    71
    8
    R417a
    Any one have experience with R22 to R417a conversions. What is the best superheat value for 417A ?.
    Any particualr problems encountered with 417a ?
    reefer
    Oct 2005
    Canada
    35
    R134 flooded system Surge Drum
    Anyone familiar with tables for sizing
    surge drums for 134a refrigerant, or supplier.
    typical use of the surge drum is for flooding
    the evaporator and protect the compressor from liquid carry over.
    Ammonia and R22 are the most common refrigerant we typically design for in our industrial refrigeration company; but the consultant is insisting on 134a refrigerant.
    I have my own spreadsheet to size the vessel, simply I would like to verify my calc. with with someone who had a similar experience
    Oct 2004
    Scotland
    1,454
    21
    Re: R417a
    Did you just close your eyes and stick a pin on the screen to determin where to post this question????
    Chillin
    and go get a cuppa
    Aug 2005
    5,302
    Re: R417a
    Hi Camille,
    If you can provide the operating conditions and capacity requirements, I will review the surge drum sizing using my methods for comparison.
    Best Regards,
    US Iceman
    Sep 2005
    uk
    499
    21
    Re: R417a
    Quote Originally Posted by chillin out
    Chillin
    lol. its getting about a bit isnt it.
    Takes a licking, keeps on ticking.
    Feb 2006
    Mauritius
    22
    Re: R417a
    Hi Camille,
    If it's for a new system, especially industrial - which you will use for several years - I would recommend you think again about going with R 134a. Its high warming index has already reduced its use in small systems, and its future may not be very bright.
    Seek advice also from your country's environment ministry/dept to make sure you can go according to your consultant's recommendation.
    Mar 2006
    West Midlands
    15
    Re: R417a
    hi reefer, have done quite a few R417a conversions on split a/c systems and had very little problems. i used isceon 59 which is now allocated as R417a and if you contact isceon they have loads of info. usually set superheat at as near to 7oC as possible but with preset capillaries can be a bit hit and miss and when changing from R22 to R417a we worked on manufacturers refrigerant charging info plus 10% and was never far off.
    john.
    Oct 2005
    Canada
    35
    Apr 2004
    Pakistan
    44
    129
    21
    Re: R417a
    In many systems of R-22 R-417A is being replaced directly by change of oil and it exhibits almost same properties as those of R-22 and it is termed as direct replacement of R-22 but there is a temperature glide problem which is not so much to trouble any1 you may search R-417A by name of ISCEON-59(it is member of isceon series) in google and personally i am amazed as it is not used instead of R-407C
    Our nose is our personal air-conditioning system: it warms cold air, cools hot air and filters impurities
    Old working dog's Avatar
    Old working dog Guest
    Cool Re: R417a
    I have used 417a now for over 3 years now in Las Vegas And have had little or no issues.
    Have been using after replacing compressors with routine clean outs. Even seems to work in the desert heat..
    Oct 2005
    Canada
    35
    Re: R417a
    R417A is a zeotropic three-component blend [composed of 46.6% R-125, 50% R-134a, 3.4% R-600 or butane] ,is an effective refrigerant for process cooling. and cold storage from +10F to -30F, its effectiveness at higher temperatures ,giving the added benefit of lower discharge temperatures
    Comparison to R22:
    The best substitute for R22 with Zero ODP, R417A is unique non-ozone depleting long-term replacement for R22.
    R417A can replace R22 without unit modification, no change of oil , can be used in compressors designed for R22, can be used with Mineral ,AB or POE oils, is non-flammable and rated Al by ASHRAE, is comparable to R22 in terms of performance.
    Properties R22 R417A
    ODP 0.05 0 0 0
    Boiling Point (F') -41.4 -43.3
    Temperature Glide (R) 0 10.0
    Critical Temperature 205 194
    Condensing Temperature
    at 375 psi (absolute) 145 154
    Refrigeration Capacity (%) 100 97
    C.O.P.(%) 100 112
    Discharge Gas Temp. (R) - -16.2
    Lubricants MO,AB,POE
    Camille Zabbal
  1. R 417 A direct replacement of R 22
    By abbasi in forum Refrigerants
    Last Post: 08-09-2011, 12:47 AM