Thread: Defrost question
10-10-2013, 12:05 AM #1
Defrost timer 2 part question
To check timer with ohm meter do you take readings across 3 and 4 and also on automatic defrost timer I had voltage to defrost heater but no heat was being generated would the problem be the defrost terminating thermostat could be open?
10-10-2013, 11:21 AM #2
Re: Defrost timer 2 part question
Defrost timers work differently.
But in general they tend to be a 2 pole switch. Switched in
one direction they run the refrigeration circuit, switched in
the other direction they run the defrost circuit.
Your question is a bit vague but you would expect to see
the timer to switch and the connections need to be correct.
Voltage measured or testing the continuity (with power disconnected)
should show you if it is working or not.
Rob
10-10-2013, 02:11 PM #3
Defrost question
I have voltage to defrost heater but no heat is being generated would the problem be the defrost terminating switch
10-10-2013, 02:16 PM #4
Re: Defrost question
We don't know
If you have voltage to your heater, is the heater OK?
If you have voltage to your heater, is there a neutral?
If you have voltage to your heater, do you have voltage through the defrost termination?
Vague answers to a vague question
Rob
10-10-2013, 05:00 PM #5
Test question
10-10-2013, 06:36 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
How do you know that you have voltage to the heater?
How did you measure it?
Having one end at voltage higher than ground and another not conected to anything, doesnt mean that you have "voltage" to the heater, since heater only works at voltage diferential.
11-10-2013, 06:04 PM #7
You could check if you have continuity through the heating element to prove the heater.
The last thing to leave an engineer is pride!!