    Insulation testing



    When you guys are doing a service/maintenance do you use a megger?On machines that have been poorly looked after for example have dirty coils,hot running compressors i always get very low readings(below 250 Mohms).incidently I tested equipment that hadn't been used for years so was cold and they to had very low readings?!The machines I'm on about are fridges and freezers.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Insulation testing

    If it is running, [poorly or otherwise] nothing is tripping, I dont see any reason for a megger testing.

  3. #3
    Join Date
    Jan 2013
    Location
    scotland
    Age
    44
    Posts
    52
    Rep Power
    12

    Re: Insulation testing

    I've never used a megger in previous jobs but my new work place insist?Like I said a few machines that I've been to have been in poor condition and running 'hot' due to dirty condensers.Im convinced that this messes up resistance readings.Also units that have been dormant for months and just switched on give false readings as when they 'warm' up the resistance readings are above normal.I don't see the need for it?!

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Insulation testing

    I am astonished with previous comments, " never used a meggar, if it runs why test ". Multi-meters are a joke if used for ground leakage testing. I have had megger variants for all my years in the trade
    Ever heard of criminal liability if a client is injured or at worst killed by an appliance that you have recently serviced.
    I bet that no has ever done a loop impendence circuit test on a new installation.

    grumpy magoo

  5. #5
    Join Date
    Nov 2013
    Location
    Indonesia
    Age
    47
    Posts
    2
    Rep Power
    0

    Re: Insulation testing

    Dear All,

    In my plant, usually we will test the insulation resistance of the cabling and motor after the equipment is idle for quite some time.

    We had case (a few days ago in fact) where the equipment had been idle for quite a prolonged period and when it was tested, the reading is low. We tried to test-run the equipment and the motor got burnt.
    Therefore, I think it is better to test it first before operate the equipment.

    Anggoro YN

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Insulation testing

    Quote Originally Posted by Magoo View Post
    I am astonished with previous comments, " never used a meggar, if it runs why test ". Multi-meters are a joke if used for ground leakage testing. I have had megger variants for all my years in the trade
    Ever heard of criminal liability if a client is injured or at worst killed by an appliance that you have recently serviced.
    I bet that no has ever done a loop impendence circuit test on a new installation.

    grumpy magoo
    Please dont get grumpy, have a cold pint and relex.

    Megger testing is a way to fined faults in electrical circuits.
    Loop testing is to make sure eart impedance is ok and RCD will protect in case of a fault.

    I always check new electric instalation with a megger and the sparky who supply the currant to the new electric board must check loop testing.

    i dont do regular megger testing but i do test RCD for proper function.

  7. #7
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    78
    Posts
    195
    Rep Power
    17

    Re: Insulation testing

    I would recommend you don't check compressors with a mega tester. The high voltages coupled with the fact a mega tester uses a modulated DC test output can blow any thermistors that might be integrated with the motor windings for thermal protection. The junction of most solid state devices won't survive a mega test unless it's specifically designed for it. The same would be true for any machine that has electronic controllers built in. If you really must do a mega test then I'd only use a 250volt test and definately not on the 500v, 1kV or 5kV range and always have it in mind that this kind of testing can cause faults as easily as it can find them.

    With regards to seeing leakage, it's also worth thinking about what else could have an effect on the test results. Most modern day items have noise supressors and surge/spike arrestors built into the early stages of the power supplies. These devices all have a clamping voltage that could easily be exceeded during a Mega test and as soon as they start to conduct they allow a current to flow to earth. This will lead you to believe there's a fault when there isn't because the earth is a functional connection as well as a protective one. Also altitude can effect insulation readings so the pressure (or vacuum) in a refrigeration system will almost certainly have a hand in the results seen during testing.

    An insulation measurement of 250Mohms mentioned in the first post is 250 times higher than the figure of 1Mohm which is generally considered as the absolute minimum requirement (assuming the result was obtained at the normal running voltage). Why do you describe the result as low and why do you think it needs addressing?

    If the concern is for user safety I'd suggest maybe rather focus on making sure the circuit is going to perform if a fault occurs. An earth impedance test and an RCD test would be of value for this.
    Last edited by Frikkie; 17-11-2013 at 06:54 PM.

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Insulation testing

    Frikke.
    Your point may be relevant on small stuff?
    But not on most of the kit i work on.
    Even the motor manufactures sometimes give expected values.
    If you are worried about frying components don't do it.

    But I suspect most on this forum know what they are doing.

    The trick is to disconnect that which you don't want included in the test. Meggars are a valuable tool in the correct hands.

    So I have to disagree with the bulk of your statement.
    Grizzly

  9. #9
    Join Date
    Jul 2009
    Location
    South Africa
    Age
    78
    Posts
    195
    Rep Power
    17

    Re: Insulation testing

    Hello Grizzly.

    I agree a mega tester is a valuable tool in the right hands but I fear there are many hands they should not be in. You are also right I was thinking of smaller dome compressors as well. Please forgive me if my advice is misleading and I certainly wouldn't imply the people of this forum don't know what they're doing. I usually type at the same time as I think and my English can be difficult so sometimes my posts can be somewhat chaos.


    I am still hesitant about how much value they would be as a tool for general refrigeration servicing or maintenance. You could use an earth leakage clamp meter around the live and neutral wires simultaneously to get a precise value of current leaking to earth under actual running conditions, this would be more accurate and it wouldn't have any of the destructive risks the using a mega tester would have.

    You can do this clamp test on a three phase machine or motor as well as long as you clamp all the wires including the neutral if one is connected.
    Last edited by Frikkie; 17-11-2013 at 07:47 PM.

  10. #10
    Join Date
    Mar 2012
    Location
    italy
    Age
    67
    Posts
    78
    Rep Power
    13

    Re: Insulation testing

    After many years of testing with megger insulation of compressors, do tests and recorded periodically, we can monitor the increase of moisture in the circuit and the insulation of the compressor was not only to earth but also between windings part winding, so from my experience if the megger is used with knowledge of the facts is a useful tool for routine maintenance

    regards Mark

  11. #11
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Insulation testing

    Always use meggar on a cold compressor and check ohms resistenances because when compressor has been running the resistenance goes weak with heat. I did check once a compressor with 1000v and at same time put a mutimeter on the thermal overload pins which were connected to kriwan therms and i got induced voltage of 36volts dc.but nothing happen to them. And yoh are not suppose to put more than 7 volts. There fore when machines are running with 400v. Thr thermal overloads are getting induced voltages

  12. #12
    Join Date
    Dec 2013
    Location
    USA
    Posts
    5
    Rep Power
    0

    Re: Insulation testing

    When I was first trained to use a megger 250 meg ohms was considered more then acceptable by manufacturers standards. Machines with these values ran fine for years afterwards and no change was noted during subsequent inspections. This isn't implying changes don't occur and the reason why they're done.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Insulation testing

    Yesterday, I was testing insulation resistance on one Maneurop scroll compressor SZ090S4VC which is more than 5 years old and failed mechanically It has seen lot of overheating since paint on dome is wrinkled and brown. Insulation resistance was measured with 500V and after 15 sec it is stabilised at OL (out of measuring range wich is 4GΩ at 500V test voltage for used instrument Uni-T511) for each winding.
    Today modern winding insulation resistance could reach number of 20GΩ in new product and during working life of that product could stay easily in region above 1GΩ.
    Below that number we have indication that insulation or condition in motor is deteriorating more than it should be.

    Therefore, it is of great help to make insulation test of motors at comisioning and note measured data for future reference.

    By new standards IEEE 43-2000, not aceptable winding insulation is below 100MΩ.

    http://www.transcat.com/technical-reference/IEEE.aspx
    Last edited by nike123; 05-01-2014 at 10:44 AM.