    Carrier HAP - Air Flow rates



    Hi,

    For a heat load estimated with HAP, the fresh air requirment was 35lps, and HAP ouput shows that the supply air as 139L/s. Now my question is whether the AHU fan should be sized for 139L/s or the considering both fresh air and supply air, which is 35 + 139 Lps.
    Systems Design Report.pdf
    Thanks
    Nevin



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Carrier HAP - Air Flow rates

    Quote Originally Posted by nevinjohn View Post
    Hi,

    For a heat load estimated with HAP, the fresh air requirment was 35lps, and HAP ouput shows that the supply air as 139L/s. Now my question is whether the AHU fan should be sized for 139L/s or the considering both fresh air and supply air, which is 35 + 139 Lps.
    Systems Design Report.pdf
    Thanks
    Nevin
    Hello Nevinjohn

    The Air System Sizing Summary reports the total supply fan airflow rate of 139 L/s which includes the 35L/s of Outdoor Ventilation Air.
    Note the Supply Fan Sizing Data section lists the 139 L/s as the total supply air volume.
    I trust this helps.

    best regards
    moideen-Dubai