    I don't often get stuck but......



    This has happened a couple of times to me lately.....Ive fitted a replacement controller one was an elliwell id series and one supplied by foster, an LAE.
    So I wired them in as per usual and connected up the new probes and when I switched the thing on, the temperature read 104 degrees. So I stuck a generic electric defrost controller on and no probs!!

    Anyone had this happen to them and any ideas why??

    And while I'm at it....what is the reason for having 12/24v supplies to the controllers instead of 240v? It can't be to save electricity and if I have to change one I just bypass the transformer and no problems. (you can have only so many spare controllers on the van so I just have 240v supply ones)
    There must be a reason but I'm gosh darned if I can think of any kind of engineering advantage....someone please enlighten me

    Oh yeah, one other thing...why would a bog standard double door upright fridge need three very expensive pcb's and a spaghetti junction of wiring to turn the compressor and evap. fans on and off?.....off cycle defrost too!

    To save the customer hundreds of pounds I bypass all the electronic rubbish that for instance Gram insist on fitting to their fridges (I do think they are well made, If unnecessarily electrically complicated) and just run the thing from a carel controller which is quite capable of handling the switching load.

    Maybe I'm missing something...maybe I'm not...I don't know lol



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: I don't often get stuck but......

    Mark up on spares...
    Guaranteed spares sales when "standard" isn't the standard and markup on spares...


    (I used to just be cynical, nowadays I'm old and cynical.)

  3. #3
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31

    Re: I don't often get stuck but......

    It is about lethal voltages, 24v is a far safer operating voltage.
    Although AC has the benefit of lower volt drop over distance, electronic components are essentially mostly DC therefore the AC controller will have to convert adding to cost and complexity.
    AC switching induces magnetism and varying current magnitude which can have an impact on electronics.

    As for your probe problem you probably have an NTC on a PTC controller or vice versa.
    I love the smell of Ammonia in the morning!

  4. #4
    Join Date
    May 2005
    Location
    london
    Age
    59
    Posts
    29
    Rep Power
    0

    Re: I don't often get stuck but......

    Quote Originally Posted by hookster View Post
    It is about lethal voltages, 24v is a far safer operating voltage.
    Although AC has the benefit of lower volt drop over distance, electronic components are essentially mostly DC therefore the AC controller will have to convert adding to cost and complexity.
    AC switching induces magnetism and varying current magnitude which can have an impact on electronics.

    As for your probe problem you probably have an NTC on a PTC controller or vice versa.
    NTC/PTC.....yeah I tried changing the parameters (1st thing I thought of) but made no difference. Maybe I was supplied with incompatible probes....still not sure.

    If 240 is viewed as too dangerous, then fair enough....but they all have to have a 240 feed to them for the compressor/defrost/fan relays. So I don't think safety is an issue and 240 v controllers work fine (mostly).

    Plus I can get a new controller for under 30 quid which will replace much more expensive ones.

  5. #5
    Join Date
    May 2005
    Location
    london
    Age
    59
    Posts
    29
    Rep Power
    0

    Re: I don't often get stuck but......

    Quote Originally Posted by The Viking View Post
    Mark up on spares...
    Guaranteed spares sales when "standard" isn't the standard and markup on spares...


    (I used to just be cynical, nowadays I'm old and cynical.)
    But we can convert them to standard **evil laugh**

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: I don't often get stuck but......

    After changing of probe type in parameters you need to turn power supply off and than on for Eliwell ID controlers.
    Then, if you have original Eliwell probes PTC or NTC type, it will show correct temperatures.

    For LAE, I don't know and I don't care, since I never ever using them. It is enough that Eliwell is Maid in PRC. I don't need another PRC s..t

  7. #7
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,045
    Rep Power
    35

    Re: I don't often get stuck but......

    Quote Originally Posted by sokold View Post
    And while I'm at it....what is the reason for having 12/24v supplies to the controllers instead of 240v? It can't be to save electricity and if I have to change one I just bypass the transformer and no problems. (you can have only so many spare controllers on the van so I just have 240v supply ones)
    There must be a reason but I'm gosh darned if I can think of any kind of engineering advantage....someone please enlighten me
    Welcome to the path of enlightenment grasshopper. Well, I'm no Mr Miyagi but after working on a refrigerated van with an LAE controller it made we wonder if the 12V version was made to go in vehicles as well.

    Cheers, Andy.
    Health and safety first..........unless I'm in a hurry.

  8. #8
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: I don't often get stuck but......

    .

    I find one of these

    Hammer.jpg

    helps with problematic controllers.

    Sort of a stress reliever


    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  9. #9
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: I don't often get stuck but......

    Hi Rob
    A very handy tool that's for sure.
    Paul

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: I don't often get stuck but......

    I call it "persuader"!

  11. #11
    Join Date
    May 2005
    Location
    london
    Age
    59
    Posts
    29
    Rep Power
    0

    Re: I don't often get stuck but......

    Quote Originally Posted by nike123 View Post
    After changing of probe type in parameters you need to turn power supply off and than on for Eliwell ID controlers.
    Then, if you have original Eliwell probes PTC or NTC type, it will show correct temperatures.

    For LAE, I don't know and I don't care, since I never ever using them. It is enough that Eliwell is Maid in PRC. I don't need another PRC s..t
    good point about turning them on and off, I'm fairly sure I did that....but to be honest I can't remember. .....Stored away in the memory bank for next time

    Don't get me started on Chinese made kit....just look at the decline in quality of danfoss mag valves...they used to be ultra reliable, now they're a liability on every system they're installed on. They were even selling replacement O ring kits for them a while ago because of the high failure rate. But what are we meant to do...use Parker stuff

  12. #12
    Join Date
    May 2005
    Location
    london
    Age
    59
    Posts
    29
    Rep Power
    0

    Re: I don't often get stuck but......

    Quote Originally Posted by Tayters View Post
    Welcome to the path of enlightenment grasshopper. Well, I'm no Mr Miyagi but after working on a refrigerated van with an LAE controller it made we wonder if the 12V version was made to go in vehicles as well.

    Cheers, Andy.
    I've managed to avoid transport refrigeration all these years...I guess they have some sort on inverter to convert dc to ac...so that would make sense

  13. #13
    Join Date
    May 2005
    Location
    london
    Age
    59
    Posts
    29
    Rep Power
    0

    Re: I don't often get stuck but......

    Quote Originally Posted by Rob White View Post
    .

    I find one of these

    Hammer.jpg

    helps with problematic controllers.

    Sort of a stress reliever


    Rob

    .
    Turbo torches work well too

  14. #14
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: I don't often get stuck but......

    Quote Originally Posted by sokold View Post
    Turbo torches work well too
    Thats taking it to a whole new level

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  15. #15
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: I don't often get stuck but......

    I think years ago when the controllers first came out there wasn't room for a transformer in them but now they can put a solid state doodah in it thats much smaller.
    Mostly found in Oxfordshire, UK :)

  16. #16
    Join Date
    Jan 2008
    Location
    north west
    Age
    42
    Posts
    234
    Rep Power
    19

    Re: I don't often get stuck but......

    The dixell universal j and r come with 240 and 12v optional in the same unit so no need to carry loads, although I find them a bit over the top with the amount of parameter settings.
    The last thing to leave an engineer is pride!!

  17. #17
    Join Date
    May 2005
    Location
    london
    Age
    59
    Posts
    29
    Rep Power
    0

    Re: I don't often get stuck but......

    doodah's have come a long way...it makes sense not have a separate transformer in the chain...one less thing to go overheat and go wrong ! Cheers for that

  18. #18
    Join Date
    May 2005
    Location
    london
    Age
    59
    Posts
    29
    Rep Power
    0

    Re: I don't often get stuck but......

    Quote Originally Posted by 1mikeefc1 View Post
    The dixell universal j and r come with 240 and 12v optional in the same unit so no need to carry loads, although I find them a bit over the top with the amount of parameter settings.
    yeah I like the simpler ones too, life is hard enough!

  19. #19
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    425
    Rep Power
    20

    Re: I don't often get stuck but......

    There's two or three types of ntc probes that lae use, sometimes you can adjust the type of ntc, sometimes you can't, sometimes they are stupid enough to allow you to have two different types of ntc probes connected. Makes defrost termination interesting - seen a few scorched coldroom ceilings.
    On some of the early polar fridges the supposed ptc probes that they have are not compatible with any eliwell, dixell etc. so you have to muck about changing the probes as well when the controller packs up.

  20. #20
    Join Date
    May 2005
    Location
    london
    Age
    59
    Posts
    29
    Rep Power
    0

    Re: I don't often get stuck but......

    [QUOTE=Andy AC;286855]There's two or three types of ntc probes that lae use, sometimes you can adjust the type of ntc, sometimes you can't, sometimes they are stupid enough to allow you to have two different types of ntc probes connected. Makes defrost termination interesting - seen a few scorched coldroom ceilings.
    On some of the early polar fridges the supposed ptc probes that they have are not compatible with any eliwell, dixell etc. so you have to muck about changing the probes as well when the controller packs up.

    That makes sense, every controller/probe problem I've had has been when they're supplied loose, i.e. controller in a plastic zip bag with (usually ridiculously long) probes that look like they've been wound round someones hand. Buy them in a box with the probes and they always work. I guess the answer is to never get spares from manufacturers! I do believe it's mystery solved

    Thanks to every one who replied, I really appreciate it

    cheers Tim

  21. #21
    Join Date
    Jul 2011
    Location
    UK
    Age
    75
    Posts
    6
    Rep Power
    0

    Re: I don't often get stuck but......

    As already pointed out, if you change the probe type on an Eliwell controller between NTC and PTC you have to remember to power down and power up again to update the change.

    Parameter H00 - 0 = PTC, 1 = NTC

    Why both 12V & 230V ? Simple

    In the early days of these controllers, transformers were too large to fit inside, so they were designed as 12V with external transformers. These days we have transformers small enough to fit inside and OEM manufacturers prefer 230V as it's one less component to wire

    24V is rarely asked for apart from control panels

    If you have a problem with carrying both 12V & 230V on your van, consider the Dixell Universal-R service replacement controller. It has connections for both 12V & 230V

  22. #22
    Join Date
    May 2008
    Location
    ENGLAND
    Posts
    61
    Rep Power
    16

    Re: I don't often get stuck but......

    Quote Originally Posted by 1mikeefc1 View Post
    The dixell universal j and r come with 240 and 12v optional in the same unit so no need to carry loads, although I find them a bit over the top with the amount of parameter settings.
    Yes Mike Dixell Universal R very handy spare to have in the van always have a couple spare just in case!

  23. #23
    Join Date
    Aug 2001
    Location
    Nr Manchester, UK
    Age
    54
    Posts
    36
    Rep Power
    0

    Re: I don't often get stuck but......

    I believe that if the controller is 24v powered then it becomes a whole load easier to get through the CE marking process as there is no mains present.