    Using the formula for calculating the maximum theoretical COP, I mathematically come to the conclusion that it is the maximum COP per stage, while adding stage seems to be much more efficient.
    I've seen that formula in many places, here is one of them:
    http://en.wikipedia.org/wiki/Coefficient_of_performance
    So I used:
    Th=24C=297K
    Tc=4C=277K
    COP (heating) = Th/(Th-+Tc) = 297/(297-277) = 297/20 = 14.85
    COP (cooling) = Th/(Th-+Tc) = 277/(297-277) = 277/20 = 13.85
    I'm cool with that.
    I'll assume it takes a 1 joule to raise the temperature by 1 degree. I know it's no real world value, but that is a constant and therefore don't affect the end result which is a percentage.
    While I cool 13.85 degrees for 1 joule of energy provided to the system, I calculate the amount of energy I need to provide for 20 degrees, which is 1j*20K/13.85K = 1.444 joule
    Now I do the very same process for in two steps, i.e. (Th, Tc) of (4, 14) and (14, 24) instead of one (4, 24) step.
    COP (cooling step 1) = Th/(Th-+Tc) = 277/(287-277) = 277/10 = 27.7
    COP (cooling step 2) = Th/(Th-+Tc) = 287/(297-277) = 287/10 = 28.7
    1j*10K/27.7K = 0.361
    1j*10K/28.7K = 0.348
    When I ad the energy required by both step, I get (0.361 + 0.348) = 0.709 joules.
    That is 50.87% more efficient.
    Four steps (5 Kelvin each) results in only 0.351 joules required, for the very same cooling.
    As for heating, the same kind of calculation shoes slightly higher COP.
    Approaching 0 K (of temperature differential), there is nearly no energy required for all the cooling, which would also mean that it would take an infinite amount of space for the equipment and an infinite amount of time to do the cooling.
    I know that the real world isn't as perfect as the theory and that there are losses, but it seems that very significant energy saving could be archived. While also significantly increasing the price of the equipment, it looks like it could be worth it, at least for high temperature differentials, like a freezer in summer time, or heating indoor space during winter.
    I've seen multi-stage compressors, with in-between pressure(s), where there is a theoretical gain in efficiency for each stage that is added. After 4 or 5 stages, though, it's becomes so very insignificant. Yet, it is significant enough to be manufactured and used in industries.
    The only multi-stage heat pump I've seen seems to refer either to a dual-speed compressor; two independent heat pumps, one runs more continuously and only the other start and stop as the temperature requires it so as to save on start-up and stabilization of the system; and some with drying stage of some sort...
    Therefore, my final assumption, or my assumption so far, is that I am missing something. I misunderstand the formula, its definition, or some basic concept, or perhaps my math is wrong somewhere.
    May someone please either tell me how great of an idea this is or, more likely, point out what I am missing, where my analysis fails, or where it is actually implemented?
    Nov 2008
    136
    Re: Highest theorical COP
    your theory looks good, an easy way is energy in KW electricity to KW refirgeration . eg york chiller at part load has 100 kw of electrical energy in to make 700 kw of refrigeration. COP 7
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2007
    Hampshire
    438
    32
    Must be a phenomenal chiller!! Part load COP of 7 I think the salesman has been telling porky pies!
    Mar 2009
    KZN, South Africa
    64
    2,212
    COP = (What you get) / (What you pay for) Do make sure that you inject ALL the energy (power) paid for - compressor, fans, pumps, etc.
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2008
    u.a.e
    49
    412
    23
    Quote Originally Posted by hookster View Post
    It is real. The latest Mitsubishi centrifugal ETA series chiller claim full load cop is 6.4 and part load cop is 10.2 and maximum part load cop is 23.8!
    hookster's Avatar
    Apr 2007
    Hampshire
    438
    32
    I understand theoretical part load COP sounds good on manufacturer blurbs! But the reality is that this is marketing bull. You have a massive chunk of unused capital equipment sitting unused to get these high COP figures.
    They are usually achieved at almost impossible conditions to replicate (enthalpy of Air in / air out etc.) in the real world besides for a split second in time
    There is no real point to part load conditions, if they are not a large percentage of operating time.
    Then you need to question why this was designed for small peak loads anyway. The move to SEER rating gives a better true interpretation of operating conditions although this is not perfect either.
    Oct 2003
    5,630
    34
    Info abouth this wonderful machine?
    Oct 2013
    Canada
    4
    Thanks for your replys. This is going slightly off topic so I would like to bring attention back to the essence of what I was asking.
    Quote Originally Posted by desA View Post
    I understand that in the real world, there are losses. Some here are talking about whether some figure are or can be archived in the real world. One could add that the cost of the parts should be included in the practicability of such implementation, which is true, important to remember, but that does not address the matter in question.
    Even though energy consumed by fans to speed and energy loss form the compressor or pump affect the overall COP of a system we would build, it has nothing to do with the efficiency of the "cooling/heating" itself.
    Quote Originally Posted by 7171 View Post
    Approaching 0 K (of temperature differential), there is nearly no energy required (edit: the COP approach infinity) for all the cooling, which would also mean that it would take an infinite amount of space for the equipment and an infinite amount of time to do the cooling.
    Pump and compressor have their own efficiency, which will affect the overall efficiency of a device in the real world, but not the efficiency on the cooling or heating effect itself. Those are outside the scope of this thread.
    My interrogation here is about theory, i.e. what really is the maximum theatrical amount of energy we can move with a given amount of... "work" (or electricity or energy, or whatever you want to call it)?
    From my understanding, the Carnot cycle is defined as that "maximum", either using work to move heat, or converting a temperature differential into work. However, using the formula that theory proposes, I seem to prove that it can't describe the maximum it claims to describe, but at best what .
    So, logic tells me that at least one of the following statement would be true:
    1. I misunderstand the Carnot's theorem. (e.g. it does not describe the maximum efficiency)
    2. There is a flaw in my analysis. (e.g. Step X does not lead to Y)
    3. I miscalculated something.
    4. The Carnot's theorem proves itself to be wrong.
    5. I am missing something really important here.
    Which option do you vote for? And how do you back your vote?
    Aug 2009
    New Zealand
    2,554
    26
    Just a simple one first, did you add the work done from the previous stage, to the work needed to be done by the next stage. Or does this extra energy within the the stages magically dis-appear.
    Oct 2013
    Canada
    4
    Quote Originally Posted by mad fridgie View Post
    Using the wrong formula, adding the heat from the previous step may have affected cooling negatively, while for heating, it would just have increase the efficiency even further.
    HOWEVER:
    Over the fact that I made a mistake in:
    COP (heating) = Th/(Th-+Tc) = 277/(297-277) = 277/20 = 13.85
    which should have been
    COP (cooling) = Tc/(Th-+Tc) = 277/(297-277) = 277/20 = 13.85
    (which I couldn't edit,)
    there is the fact that, even though the formula for the COP is correct, the Carnot's theorem that defines the maximum efficiency is 1-(Th/Tc), which is different from the one for the COP.
    With the right formula, more energy is required as steps are added. What a surprise!
    Thanks a lot for your pointer. The revision brought me to realise I wasn't using the right formula in the first place.
    COP: http://fr.wikipedia.org/wiki/Coefficient_de_performance
    Carnot's theorem: http://en.wikipedia.org/wiki/Carnot%...rmodynamics%29
    Oct 2013
    Canada
    4
    The energy doesn't magically disappear. In the example, each stage require respectively 0.361 and 0.348 joules for a total of 0.709 joules, which compares to 1.444 joules when done in one step.
    It seems that I didn't think much before writing my last message because both formulae are basically the same i.e. the COP (Th/(Th-Tc)) is the reciprocal of the efficiency (1-(Tc/Th)). I had also wrote 1-(Th/Tc) instead 1-(Tc/Th).
    So I'm still in the same boat. Any ideas?