    Daikin rqyq140py1



    Hi fellas ,, need a bit of help .. I'm going to a job tomorow , a daikin rqyq140py1 was going out on E3 .. The engineer checked hp sp2 all ok , switch not open circuit , checked hp s1ph transducer and Dc voltage ok and corresponds to Lp .. He has replaced main pcb .. But upon starting unit up it goes back into E3 again .. ??? Any knowledge would be grateful before I get to site .. Cheers



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin rqyq140py1

    “E3” Outdoor Unit: Actuation of High Pressure Switch
    Remote
    Controller
    Display
    E3
    Applicable
    Models
    RQYQ-PY1
    RQEQ-PY1
    Method of
    Malfunction
    Detection
    Use the protection device circuit to detect continuity at the high pressure switch.
    Malfunction
    Decision
    Conditions
    Abnormality is detected when the contact of the high pressure protection switch opens.
    (Reference) Operating pressure of high pressure switch
    Operating pressure:4.0MPa
    Reset pressure: 3.0MPa
    Supposed
    Causes
    „ Actuation of outdoor unit high pressure switch
    „ Defect of high pressure switch
    „ Defect of outdoor unit main PCB (A1P)
    „ Instantaneous power failure
    „ Faulty high pressure sensor

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin rqyq140py1


  4. #4
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Daikin rqyq140py1

    Well the engineer put it down to Pcb after doing all the checks , which I'm told he's replaced but e3 still coming up

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin rqyq140py1

    stick a gauge on to moniter the actual pressure- digital gauges will show min/max pressures- also instantaneous power failure??- reset the power on the indoor ringmain and the outdoor power

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin rqyq140py1

    And watch for the outdoor fan switching from high speed to low speed when the compressor is full speed.

    Symptoms of a dodgy ambient thermister.

  7. #7
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Daikin rqyq140py1

    Well after checking most components , I found that it was an earth leakage .. Comp shot and down to earth .. God knows why it was flagging up an e3 fault .. But that's what it was

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin rqyq140py1

    u did test it on the comp pins with the lead disconnected-
    Quote Originally Posted by Darrenp View Post
    Well after checking most components , I found that it was an earth leakage .. Comp shot and down to earth .. God knows why it was flagging up an e3 fault .. But that's what it was

  9. #9
    Join Date
    Feb 2013
    Location
    Uk
    Age
    52
    Posts
    135
    Rep Power
    13

    Re: Daikin rqyq140py1

    For sure ... Caput mate