    Fujitsu hot fan motor



    Hi all has any one had a fault on a fujitsu when control locks it self on. We had this found fuse blown on power board indoor unit and fan motor had gone , replacement parts come down stripped unit replaced fan motor, power board, powered up and tested.the same control locked again and new fan motor did not run just got really hot .we thinking it could be a fault motor which has come down. But the control locking its self .



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Fujitsu hot fan motor

    if its an ac fan then check the capacitor

  3. #3
    Join Date
    Apr 2010
    Location
    Jersey c i
    Posts
    82
    Rep Power
    15

    Re: Fujitsu hot fan motor

    Yeah it's an AC fan checked capacitor 15 mf. We have one outdoor unit which looks like a vrv. Supplying two ducted units it's the slave unit which had the blown power board, and failed fan . Going to try anther motor tomorrow. And may run in a new cable as it's a mess and we are getting power from neural to earth. From 110 to 64 volts
    Last edited by Paul a/c; 02-10-2013 at 09:18 PM.

  4. #4
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Fujitsu hot fan motor

    Quote Originally Posted by Paul a/c View Post
    Going to try anther motor tomorrow. And may run in a new cable as it's a mess and we are getting power from neural to earth. From 110 to 64 volts
    Do you not think you should find out why you have voltage on the neutral before replacing fans and any more PCBs?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  5. #5
    Join Date
    Apr 2010
    Location
    Jersey c i
    Posts
    82
    Rep Power
    15

    Re: Fujitsu hot fan motor

    Going to run a new 3 core power cable from master 123 to slave 123 as it's some where here we picking up the voltage . Then bell out the cable to the roof which comes from outdoor unit to the indoor master unit , and check isolaters as well could be a neutral fault some where.

  6. #6
    Join Date
    Apr 2010
    Location
    Jersey c i
    Posts
    82
    Rep Power
    15

    Re: Fujitsu hot fan motor

    Hi all
    checked all cables today found the fault. Which was the new fan motor . The last thing you think is going to be faulty, stripped out the new faulty motor and fitted one in from a unused floor. All working great now