Results 1 to 3 of 3
-
02-10-2013, 11:11 AM #1
Mitsubishi SRK71HE-S1 AUXiliary relays & CnT contacts
Dear All,
What i'm doing:
I have two units in a computer room and I want to make a simple automation with an external thermostat for making them work on a rotation basis or in case of alarm and depending on the type of alarm to stop or run. I have not the service manual for the Mitsubishi SRK71HE-S1, so i'm unable to identify what each AUX contact or relay does.
Please help on the following if you could.
on Indoor unit:
what (XR5) contact does, how it works and do i need a special connector? is it output or input?
on Outdoor unit:
(52x1-5) What each from five AUXiliary relay does?
or if you are sure that i'll find the answer on the service manual please upload if possible.
Thanks a lot to all.
-
02-10-2013, 07:28 PM #2
Re: Mitsubishi SRK71HE-S1 AUXiliary relays & CnT contacts
best to keep em both running continuously-as by the time u buy an 2 interface kits and a dedicated run/standby panel
http://www.mediafire.com/download/en...ter_SRK-ZG.pdf
click on link above for srk50 service manual
-
03-10-2013, 07:44 AM #3
Re: Mitsubishi SRK71HE-S1 AUXiliary relays & CnT contacts
Thanks a lot for the Service Manual!! I found the info i'm looking for on page 57.
Many thanks!