Results 1 to 3 of 3
  1. #1
    spikour2011's Avatar
    spikour2011 Guest

    Mitsubishi SRK71HE-S1 AUXiliary relays & CnT contacts



    Dear All,

    What i'm doing:
    I have two units in a computer room and I want to make a simple automation with an external thermostat for making them work on a rotation basis or in case of alarm and depending on the type of alarm to stop or run. I have not the service manual for the Mitsubishi SRK71HE-S1, so i'm unable to identify what each AUX contact or relay does.

    Please help on the following if you could.

    on Indoor unit:
    what (XR5) contact does, how it works and do i need a special connector? is it output or input?

    on Outdoor unit:
    (52x1-5) What each from five AUXiliary relay does?

    or if you are sure that i'll find the answer on the service manual please upload if possible.

    Thanks a lot to all.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi SRK71HE-S1 AUXiliary relays & CnT contacts

    best to keep em both running continuously-as by the time u buy an 2 interface kits and a dedicated run/standby panel
    http://www.mediafire.com/download/en...ter_SRK-ZG.pdf
    click on link above for srk50 service manual

  3. #3
    spikour2011's Avatar
    spikour2011 Guest

    Re: Mitsubishi SRK71HE-S1 AUXiliary relays & CnT contacts

    Thanks a lot for the Service Manual!! I found the info i'm looking for on page 57.

    Many thanks!