    I am currently working on a walk in freezer about 2.5 metres square, the system is on a copeland scroll condensing unit, the problem is the suction line is freezing up outside, it's on R404a and the suction runs at 18psig and discharge at 200psig, not too far out I thought?
    There is no obvious damage to the pipes, the liquid line runs warm with a clear sight glass and the TEV isn't a block of ice? However the pipes leading into the evaporator are heavily iced up and so is the suction pipe outside.... What's going off lads?
    Cheers
    Matt



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: R404a walk in freezer help

    With your suction pipe at -27°C I'm not really surprised that the pipe surface has ice/frost on it.

    What is the suction superheat reading and is the pipework insulated at all?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2012
    Location
    Derby
    Posts
    11
    Rep Power
    0

    Re: R404a walk in freezer help

    Quote Originally Posted by Brian_UK View Post
    With your suction pipe at -27°C I'm not really surprised that the pipe surface has ice/frost on it.

    What is the suction superheat reading and is the pipework insulated at all?
    I'm due back on site on thurs to look deeper into it as it was full of products yesterday... I'll test the superheat then, but the insulation was looking a bit old if I'm honest, could it be as simple as that?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: R404a walk in freezer help

    Could be, weathers changed also.