    Glycol ice bank



    One of my custommer have Ice Bank ( Coils system in pool) Refrigerant is R717. Now output temrature of water is 0.5 C to 2 C . Compressors works only 8 Hour and stock Ice throw to coils, Then compressors stop and system use same ice for all day. Now this company wants -6C water output temp. Now question is if we add ethylene glycol %20 with water and freze this mix in -7C. can we get output -6C Water for all day ????? I never saw somethink like that. is it possible or not



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Glycol ice bank

    A little less than 20%, will suffice.
    Pumping properties and heat transfer co-efficents will change.

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Glycol ice bank

    I assume you mean -6C glycol, not water !
    I could be wrong, but the glycol may not freeze on coil like ice, so it may not last all day like ice build up.

    Correct me if I am wrong.

    What is the purpose of the chilled water, or glycol?
    Last edited by RANGER1; 01-10-2013 at 10:58 AM.

  4. #4
    Join Date
    Oct 2009
    Location
    turkey
    Age
    40
    Posts
    45
    Rep Power
    0

    Re: Glycol ice bank

    So is it possible to Freeze gylcol and store it like a ice ? ?

  5. #5
    Join Date
    Oct 2009
    Location
    turkey
    Age
    40
    Posts
    45
    Rep Power
    0

    Re: Glycol ice bank

    Quote Originally Posted by RANGER1 View Post
    I assume you mean -6C glycol, not water !
    I could be wrong, but the glycol may not freeze on coil like ice, so it may not last all day like ice build up.

    Correct me if I am wrong.

    What is the purpose of the chilled water, or glycol?
    Purpose is just use compressors 8 hour in a day and store gylcol ice (if is it possible) and use these ice for 16 hour. now system Works like that but output temperature of water is +0.5 C or +2.0 C. this water using in Water evaporaters for rooms but rooms can be +8 C minimum with +1 water. But we need +2room temperature.

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Glycol ice bank

    Yes it will freeze, not quite the same ice but close enough.
    If you want your rooms at 2 instead of 8, then you are going to need more storage, plus to make LT ice, you are going to have a lower SST, so reduced refrigeration capacity, so if 8 hours was just enough before, it will not be enough know.
    You will pumps less, reduced heat capacity out of the coils. so do not expect the same results as you did with water.
    Is the rooms used for food, or an industrial process, you may have to check that your glycol of choice is acceptable.

  7. #7
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Glycol ice bank

    Hi as mad fridgie says you will eventually freeze glycol mix but it will not be in your 8hr cycle. You could probably get fluid (glycol mix) down to -2 with continuous cycle of fridge plant. (giving up all the energy savings the ice bank was designed around) The ice bank is designed to match peak load conditions with the stored energy.

    Has room load increased since original design? Usually room evaporators are designed for smaller delta T on ice bank systems with a much larger evaporator surface area. I presume there is no defrost on the coils as they are not normally included / needed. If you lower on temperatures of fluid you may find you start getting icing.

    I would advise if room heat loads have not increased significantly to check condition of evaporators. Are they clean, door control, is air flow good, fans etc.

    If load has increased in room best option is either increase ice storage capacity and increase evaporator surface in rooms.

    Check your fluid on off temperatures to evaporators
    Check how long in daily cycle stored ice is available (I think you are using up the stored potential quicker than design)
    Check you refrigerant plant is operating correctly
    Check ice sensors are in correct positions

    Remember a usual ice bank design is 8 hours stored potential and 12 hours build during lower ambient. If the demand time exceeds this you will reduce ice build.

    The benefit of the ice bank is a lower sized refrigerant plant for the peak load demand!
    I love the smell of Ammonia in the morning!

  8. #8
    Join Date
    Oct 2009
    Location
    turkey
    Age
    40
    Posts
    45
    Rep Power
    0

    Re: Glycol ice bank

    Thanks Hook
    i Will check all you mention it and i can change eveparators (bigger ones) if need.

    My problem is This custommer wants Gylcol Ice Storage.

    I never see somethink like that i made many times -7C Gylcol / water mix Storage (witout ice)
    And use it like a battary.

    But What is Gylcol İce ? Is there any advantages Gylcol ice to Gylcol / water mix ?

Posting Permissions