    Climaveneta Chiller



    Hi All

    CVM3000 Climaveneta chiller controller, need to calibrate the common evaporator outlet temp probe. I understand configuration setpoints 120 to 135 are temp probe offsets but need to know which probes these offsets refer to, any help appreciated.

    Pavilion



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Climaveneta Chiller

    http://www.mediafire.com/download/h3...3/CVM_3000.pdf
    click on link for manual
    have you got access passwords

  3. #3
    Join Date
    Sep 2007
    Location
    UK
    Age
    60
    Posts
    45
    Rep Power
    0

    Re: Climaveneta Chiller

    Thanks Install monkey, I have this manual but the settings list does not identify the evap probes, have tried contacting Climaveneta but as usual no reply's . I have the passcode. Cheers.

  4. #4
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Climaveneta Chiller

    Hi
    you need the wiring diagram !
    st1 is probe 1 st2 is probe 2 all according to the wiring.
    usually evap inlet us connected to terminals 5+6 and outlet to 7+8 on the board
    all depending on model and no of circuits
    good luck
    Last edited by goshen; 01-10-2013 at 08:04 AM.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  5. #5
    Join Date
    Sep 2007
    Location
    UK
    Age
    60
    Posts
    45
    Rep Power
    0

    Re: Climaveneta Chiller

    Thanks Goshen, back on site next week will have a look then. Cheers.