Climaveneta Chiller
Hi All
CVM3000 Climaveneta chiller controller, need to calibrate the common evaporator outlet temp probe. I understand configuration setpoints 120 to 135 are temp probe offsets but need to know which probes these offsets refer to, any help appreciated.
Pavilion
-
28-09-2013, 03:26 PM #2
Re: Climaveneta Chiller
http://www.mediafire.com/download/h3...3/CVM_3000.pdf
click on link for manual
have you got access passwords
-
30-09-2013, 07:36 AM #3
Re: Climaveneta Chiller
Thanks Install monkey, I have this manual but the settings list does not identify the evap probes, have tried contacting Climaveneta but as usual no reply's . I have the passcode. Cheers.
-
01-10-2013, 08:01 AM #4
Re: Climaveneta Chiller
Hi
you need the wiring diagram !
st1 is probe 1 st2 is probe 2 all according to the wiring.
usually evap inlet us connected to terminals 5+6 and outlet to 7+8 on the board
all depending on model and no of circuits
good luckLast edited by goshen; 01-10-2013 at 08:04 AM.
THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
02-10-2013, 06:05 AM #5
Re: Climaveneta Chiller
Thanks Goshen, back on site next week will have a look then. Cheers.