Results 1 to 9 of 9
Thread: cold room
    Jan 2012
    ireland
    41
    15
    cold room
    Hi Guys
    Looking at a cold room in my local and compressor is burned out.Can get a compressor but is slightly larger displacement but same gas r404a.Will i have to ajust explansion valve or require new to get correct superheat.cold room set point is 3°c.Any advice.
    Sep 2003
    ISRAEL
    72
    4,248
    Re: cold room
    how much is "slightly"?
    May 2012
    59
    1,528
    36
    Re: cold room
    I agree with Chemies open question, plus I would
    advise you to look at the rating. It might be a slightly
    bigger comp but is it a low back pressure (LBP) or
    high back pressure (HBP).
    If you use a fridge compressor in a freezer application
    it might not be suitable and visa-versa for a freezer
    compressor in a fridge application.
    In principle a comp that is just slightly bigger but compatible,
    should have no issues replacing a similar but smaller comp.
    Rob
    Sep 2003
    ISRAEL
    72
    4,248
    Re: cold room
    As always Rob, you pinpoint the qustion, so I will refrase my question,
    Model and make of the old compressor and the new compressor.
    That should give us the ability to judge.
    Jan 2012
    ireland
    41
    15
    Re: cold room
    The old compressor is BA18MG-1 off a heatcaft system r404a.The new compressor has a displacement of 16 and is hbp.(don't have model on me right now).Room will be running at 3°c, worried about low back pressure and superheat on system if compressor is too different.
    Sep 2003
    ISRAEL
    72
    4,248
    Re: cold room
    Tthis is a number of a condensing unit, medium temp and the compressor displacement is 18cc.
    Looks like compressors they use are made by kirby.
    Jan 2012
    ireland
    41
    15
    Re: cold room
    Thanks new compressor is Embraco model-NT620GK.Would this do the job?
    Sep 2003
    ISRAEL
    72
    4,248
    Re: cold room
    It should work, diferences are minor, you might have to agjust the superheat but do that at one or two C above setpoint.
    Jan 2012
    ireland
    41
    15
    Re: cold room
    Thanks very much doing job 2mor let u know how it goes