25-09-2013, 07:32 PM #1
PTCR Relay blew up after installation
hi
i got window type air cond 24000 btu with reciprcating compressor bristol type
the manufacturer didnt use ptcr relay (hard start kit)
so i added one because i know its useful
i turned on the ac
and compressor started up
after 2 seconds or three
the ptcr relay blown up
and im sure that correctly wired it
why it blown up
25-09-2013, 07:52 PM #2
Re: PTCR Relay blew up after installation
hope u didnt burn your hand again
whats the compressor model nuumber and what does the wiring diagram say how its wired
25-09-2013, 07:57 PM #3
25-09-2013, 08:00 PM #4
its wired in parallel with the start and run of the capacitor
the compressor model number is
H2EB323ABKC
25-09-2013, 09:08 PM #5
http://hvac-talk.com/vbb/showthread....ion&p=16729521
came up in me search!! haha
http://www.supco.com/images/pdfs/Ult...O%20Series.pdf
they for smaller compressors
you sure that compressor is 24,000btu- ur quoted model capacity number indicates 323?
contact bristol for the correct start kit
25-09-2013, 09:12 PM #6
25-09-2013, 09:18 PM #7
was the compressor working before u fitted the capacitor?
if its siezed then it will blow it
25-09-2013, 09:22 PM #8
no
the compressor work perfectly
27-09-2013, 09:23 AM #9
i found another type
capaca
http://kpcapacitors.en.tradevv.com/p...arter+kits.htm