    York Millenium Screw Chiller



    Does anyone have fault codes for one of these chillers. Apparently, the code is showing as Low curr/HP/MP fault on the status panel.

    Thanks

    (it's 2 screw compressors-one circuit is OK)


    a problem shared is a problem halved

  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: York Millenium Screw Chiller

    Iceman

    no fault codes as such, what you see is what you get. this is a very common fault, covers motor overload(black box in compressor control cabinet0, high pressure cutout, 2 switches on compressor, one with recessed button even when tripped.
    They had a problem with the star delta contactors "bouncing" on start up and tripping the unit out
    Your start circuit is to the HP first i think
    Hope this helps
    AL

  3. #3
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: York Millenium Screw Chiller

    Thanks for that. I have to go there tomorrow to look at it. Apparently it's been going on for some time. One of the previous visits had found some sort of problem with condenser fans I think.

    Cheers
    a problem shared is a problem halved

  4. #4
    Join Date
    Apr 2006
    Location
    Habana, Cuba
    Posts
    9
    Rep Power
    0

    Re: York Millenium Screw Chiller

    Low corrent/MP/HP is the most comon fault and is for 3 resson.
    1.HP: High pressure in the sensor body of the compressor.
    2. MP: Motor Protection Modules (2ACE) in the system Power Panel. This module protects against phase to phase current imbalance, over corrent, under current, phase rotation and thermal current motor overload protection.
    Hope this help.

  5. #5
    Magic's Avatar
    Magic Guest

    Thumbs down Re: York Millenium Screw Chiller

    Hi Guys
    This is my first time writing on this forum and i am a rookie working with industrial equipments. I was hoping one of you guys can explain to me which is the correct method to remove oil from a screw compressor from a york millemium chiller.This system also has two oil separators. I would really appreciate your help,dont know where to start.

  6. #6
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: York Millenium Screw Chiller

    Quote Originally Posted by Magic View Post
    Hi Guys
    This is my first time writing on this forum and i am a rookie working with industrial equipments. I was hoping one of you guys can explain to me which is the correct method to remove oil from a screw compressor from a york millemium chiller.This system also has two oil separators. I would really appreciate your help,dont know where to start.
    Close the service valves, recover refrigerant and pressure the crankcase with nitrogen (just a few psi) and connect a line to the oil port, crack open the valve and derain the oil.
    a problem shared is a problem halved

  7. #7
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: York Millenium Screw Chiller

    Quote Originally Posted by iceman007 View Post
    Close the service valves, recover refrigerant and pressure the crankcase with nitrogen (just a few psi) and connect a line to the oil port, crack open the valve and derain the oil.
    That's taking the long road home!! Most don't even have service valves and you'll have to evacuate it afterwards!

    Shut system down and turn off the power. Put a line from the separator to your recycle cilinder on the liquid valve. Take a second line from the vapour valve to your recovery unit and a third from the recovery unit back to the chiller. Put the cilinder on a scale and if it's not going up anymore , or it's going down you've recoved the oil without loosing next to nothing of the refrigirant charge. Do keep in mind that the cilinder will have to be large enough to hold all the oil. Then take a oil charging pump and pump in the amount of oil you've recovered and just a little more, not less, not too much. Be carefull not to get any air in it!!!!

    Then put the cilinder upside down and blow the oil out, using ofn from the liquid side to the vapour side. Have the cilinder cleaned if the oil is really dirty or you can't get all out!

    Good luck!

  8. #8
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: York Millenium Screw Chiller

    Quote Originally Posted by Sanderh View Post
    That's taking the long road home!! Most don't even have service valves and you'll have to evacuate it afterwards!

    Shut system down and turn off the power. Put a line from the separator to your recycle cilinder on the liquid valve. Take a second line from the vapour valve to your recovery unit and a third from the recovery unit back to the chiller. Put the cilinder on a scale and if it's not going up anymore , or it's going down you've recoved the oil without loosing next to nothing of the refrigirant charge. Do keep in mind that the cilinder will have to be large enough to hold all the oil. Then take a oil charging pump and pump in the amount of oil you've recovered and just a little more, not less, not too much. Be carefull not to get any air in it!!!!

    Then put the cilinder upside down and blow the oil out, using ofn from the liquid side to the vapour side. Have the cilinder cleaned if the oil is really dirty or you can't get all out!

    Good luck!
    Out of interest, where would you connect the third line on the chiller, to the compressor ? or discharge line?
    a problem shared is a problem halved

  9. #9
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: York Millenium Screw Chiller

    I usually do, or the condensor/liquid line.

  10. #10
    Join Date
    Apr 2006
    Location
    Habana, Cuba
    Posts
    9
    Rep Power
    0

    Re: York Millenium Screw Chiller

    Quote Originally Posted by iceman007 View Post
    Close the service valves, recover refrigerant and pressure the crankcase with nitrogen (just a few psi) and connect a line to the oil port, crack open the valve and derain the oil.
    That procedures is OK, but always remained oil in the system, thi systems have 5 gallon of oil and for this procedures out only 3 gallon.
    Now I connet a line to the oil port and with the compressor run open the valve and drain the oil, for this procedures out of compressore 4 gallon, don´t worry if compressor run with low oil, the protection stop the compressor.
    After charge the oil (5gallon) and 1 hour after check the oil level and plug or charge if need.
    This is may way to do.

  11. #11
    haitham_york's Avatar
    haitham_york Guest

    Re: York Millenium Screw Chiller

    , I have a question I would like to answer it. I want screw chiller replacing the entrance and exit of water from the right to the left. Is much as possible in the case of non-response please provide me the title of the York factory screw. thanks

  12. #12
    paulbraz's Avatar
    paulbraz Guest

    Re: York Millenium Screw Chiller

    I have had the same fault on a york YASX0331, low current /mp/hp. checked the two hp switches all the way back to the compressor terminal box, they are made. Motor winding thermistor seem fine... The CT has error codes saying 8 = phase loss (not true, all phases are there) 4 = Miswire (also not true) changed the CT over from the other circuit and the same faults come up. The windings on the compressor seem fine... Changed the compressor boards over then smashed my head up against a brick wall for about an hour and still no joy. No literature or wiring diagrams on site, called york's (johnson's) technical support, no answer, left a couple of messages (no reply, no shocks there then). There appears to be a main board and then a slave board above that, could it be either of those? Please, someone help, my head hurts!

  13. #13
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: York Millenium Screw Chiller

    Dont know about that York, however, are all three phases present at exactly a/the controller's imputs?

  14. #14
    Join Date
    Aug 2007
    Location
    Germany
    Posts
    36
    Rep Power
    0

    Re: York Millenium Screw Chiller

    The three phase module senses current through the built in ct`s and transfers it as a 0-5V signal to the micro board. The only reason on a "good" module to trip on phase loss is, that there is no current sensed on one or two phases while the remaining one(s) do. Does the compressor start? How quickly after start does the problem occur? (refer to the fault history buffer). Have you checked the condition of the motor contactors (contacts), some might be worn out.
    Last edited by Entropie; 16-06-2009 at 09:48 PM.
    RTFM always thoroughly!
    Vacuum sucks!
    Sience rules!

  15. #15
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: York Millenium Screw Chiller

    Quote Originally Posted by paulbraz View Post
    I have had the same fault on a york YASX0331, low current /mp/hp. checked the two hp switches all the way back to the compressor terminal box, they are made. Motor winding thermistor seem fine... The CT has error codes saying 8 = phase loss (not true, all phases are there) 4 = Miswire (also not true) changed the CT over from the other circuit and the same faults come up. The windings on the compressor seem fine... Changed the compressor boards over then smashed my head up against a brick wall for about an hour and still no joy. No literature or wiring diagrams on site, called york's (johnson's) technical support, no answer, left a couple of messages (no reply, no shocks there then). There appears to be a main board and then a slave board above that, could it be either of those? Please, someone help, my head hurts!

    Entropie may be onto something check your HP switches again.
    One of the to ground will play havock with the 5v supplied!
    Grizzly
    Last edited by Grizzly; 16-06-2009 at 09:56 PM.

  16. #16
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: York Millenium Screw Chiller

    RF noise can also upset the processor, check grounding of each sensor. Also CT's can go out of balance.
    magoo

  17. #17
    fsfox's Avatar
    fsfox Guest

    Re: York Millenium Screw Chiller

    Ck contactor contacts, Repco, New Jersey has ABB

  18. #18
    frang55's Avatar
    frang55 Guest

    Re: York Millenium Screw Chiller

    Quote Originally Posted by iceman007 View Post
    Does anyone have fault codes for one of these chillers. Apparently, the code is showing as Low curr/HP/MP fault on the status panel.

    Thanks

    (it's 2 screw compressors-one circuit is OK)
    Check compressor mains supply, fuses, contactors and wiring.Check mains supply voltage is within tolerance. Check for defective current transformer. Good luck

  19. #19
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: York Millenium Screw Chiller

    Quote Originally Posted by paulbraz View Post
    I have had the same fault on a york YASX0331, low current /mp/hp. checked the two hp switches all the way back to the compressor terminal box, they are made. Motor winding thermistor seem fine... The CT has error codes saying 8 = phase loss (not true, all phases are there) 4 = Miswire (also not true) changed the CT over from the other circuit and the same faults come up. The windings on the compressor seem fine... Changed the compressor boards over then smashed my head up against a brick wall for about an hour and still no joy. No literature or wiring diagrams on site, called york's (johnson's) technical support, no answer, left a couple of messages (no reply, no shocks there then). There appears to be a main board and then a slave board above that, could it be either of those? Please, someone help, my head hurts!
    Hi u might not have a choice you will have to probably change the ct protection module ( toroied) ,
    these toroied controls do go bad !.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  20. #20
    nadsalamut's Avatar
    nadsalamut Guest

    Re: York Millenium Screw Chiller

    i woild like to know how to charge screw chiller with R407c? pleae help

  21. #21
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: York Millenium Screw Chiller

    Is it a water chiller?

    Does it have a data plate with the correct charge on it?

  22. #22
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: York Millenium Screw Chiller

    Quote Originally Posted by nadsalamut View Post
    i woild like to know how to charge screw chiller with R407c? pleae help
    If you don't know how to charge it you shouldn't be working on it
    a problem shared is a problem halved

  23. #23
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: York Millenium Screw Chiller

    Quote Originally Posted by iceman007 View Post
    If you don't know how to charge it you shouldn't be working on it
    Harsh.
    But I have to admit to thinking the same.

    Grizzly

  24. #24
    Join Date
    Jul 2001
    Location
    Good bay
    Posts
    50
    Rep Power
    24

    Re: York Millenium Screw Chiller

    Low Current/MP/HP is mostly caused due to High Pressure trip, there is a a dual HP switch installed on the compressor with a little blue push button, try to reset that. Check the MP module in the starter panel incase it shows some numbers then it is the cause of the trip. Or simply your compressor circuit breaker could be tripping which will cause the controller to trip indicating Low Current/MP/HP. Can also be caused by a high starting current due to stuck slide valve.
    Setrite

    A group of Donkey's Led by a Lion can defeat a group of Lion's led by a Donkey

  25. #25
    nadsalamut's Avatar
    nadsalamut Guest

    Re: York Millenium Screw Chiller

    its water chilled. i know that the liquid r407c has to be connected to the condenser line, close the valve and let the cylinder in the inverted position. is it correct?

  26. #26
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: York Millenium Screw Chiller

    Quote Originally Posted by nadsalamut View Post
    its water chilled. i know that the liquid r407c has to be connected to the condenser line, close the valve and let the cylinder in the inverted position. is it correct?

    R407C needs to leave the cylinder as a liquid so that the mix of different gasses it is made of stay correctly mixed. This will not happen if it leaves the bottle as a gas and may cause problems in the chillers operation.

    So basically it needs to leave the bottle as a liquid, it depends on the cylinder if it needs to be inverted, some have a dip tube that goes from the tap to the bottom of the cylinder to save turning it over, only you can tell what type of cylinder you have.

    Now the other problem you need to be very careful of is that if you dump liquid into the system you risk freezing the water in the evaporator/condensor until the system pressure is high enough so that any liquid refrigerant is above 0C. Look it up on a pressure temperature chart for R407C.

    Jon

  27. #27
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: York Millenium Screw Chiller

    Quote Originally Posted by nadsalamut View Post
    its water chilled. i know that the liquid r407c has to be connected to the condenser line, close the valve and let the cylinder in the inverted position. is it correct?
    You only need to invert the cylinder if there is no dip tube. R407C is a blend of R32, R125 and R134a, so if you take out a vapour the R32 will evporate first and that is what you will get in your chiller, EXCEPT if you are using the entire cylinder.

    Connect a line to the liquid side and run the water pumps in manual. You will need to make sure the heaters are on as well and the oil is up to temperature before the machine can start. Get some load on it and keep a close eye on the approach. For a flooded evaporator it will need to be under 1 degree. Also if you are having any oil issues (which can happen at part load) then current limit the chiller to raise the discharge superheat and watch it very carefully. Take a running log of the chiller.

    Grizzly I am harsh which is why I have got no friends, apart from the odd long distance one, but if there is a question about how to charge the machine, I can smell a damage bill. Sniff Sniff !!!!
    a problem shared is a problem halved

Similar Threads

  1. York Chiller
    By HVACGod in forum Commercial
    Replies: 12
    Last Post: 11-09-2010, 06:05 AM
  2. York Recip Millenium Chiller
    By iceman007 in forum Trouble Shooting
    Replies: 12
    Last Post: 28-07-2009, 07:21 PM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. York Open Drive Screw Chiller
    By Cofreth in forum Air Conditioning
    Replies: 4
    Last Post: 24-10-2005, 02:17 PM
  5. York process chiller repairs
    By Matt in forum Commercial
    Replies: 5
    Last Post: 23-03-2004, 11:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •