    Mitsubishi Electric air conditioner model : PUHY-200TEM-A



    Hello all,

    I have a problem with the above ac model. the fault code 4250 keeps appearing. I have changed the boards but nothing is happening. Does anyone have any idea, please!
    Thank you.



  2. #2
    Join Date
    Apr 2013
    Location
    American Samoa
    Posts
    11
    Rep Power
    0

    Re: Mitsubishi Electric air conditioner model : PUHY-200TEM-A

    In addition to fault code 4250 :
    * power to neutral is 120v and line across is 210v

    I have disconnected the compressor. There is no shortage to ground. But when I run the unit, I still get fault code 4250 displayed.

    The fan motor for the radiator panel comes on just after fault code 4250 is displayed.

  3. #3
    Join Date
    Apr 2013
    Location
    American Samoa
    Posts
    11
    Rep Power
    0

    Re: Mitsubishi Electric air conditioner model : PUHY-200TEM-A

    help, anyone please!!!!!

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Mitsubishi Electric air conditioner model : PUHY-200TEM-A

    Quote Originally Posted by minks View Post
    help, anyone please!!!!!
    A little patience my friend.

    This is a world wide forum and the members are not always on line or monitoring posts. Most of us still work for a living and visit at different times, depending where we are in the world.

    It might help if you posted a little information regarding the background to the unit and any history of faults, which will allow the members to build a better picture of your situation.

    The fault 4250 refers to a faulty power module...see the attached pdf
    Attached Files Attached Files

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi Electric air conditioner model : PUHY-200TEM-A

    U6
    (4250)
    Abnormality of power module
    Check abnormality by driving power module
    in case overcurrent is detected.
    (UF or UP error condition)
    1 Outdoor stop valve is closed.
    2 Decrease of power supply voltage
    3 Looseness, disconnection or
    converse of compressor wiring
    connection
    4 Defective compressor
    5 Defective outdoor power circuit
    board
    1 Open stop valve.
    2 Check facility of power supply.
    3 Correct the wiring (U•V•W phase) to
    compressor. Refer to page 125 and 126.
    4 Check compressor referring to page 28.
    5 Replace outdoor power circuit board.
    Last edited by install monkey; 20-09-2013 at 07:16 PM. Reason: info extracted from franks attachment

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Mitsubishi Electric air conditioner model : PUHY-200TEM-A

    Which boards have you replaced? All of the inverter pack or just certain boards?

    4250 can be caused by a number of things.

    Over current detected by the current sensor
    A short circuit on the load side just before starting the inverter operation
    Short circuit in the output wiring
    Inverter board fault
    Compressor fault.

    The fan motor for the radiator panel comes on to keep the temperature below 105C otherwise it would fault on 4260.

    Do you have an inverter checker to verify balanced output from the inverter with the compressor disconnected?
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: Mitsubishi Electric air conditioner model : PUHY-200TEM-A

    Any geckos, mice, 'roaches or other vermin in it - or evidence of same?

  8. #8
    Join Date
    Oct 2013
    Location
    Turkey
    Age
    33
    Posts
    15
    Rep Power
    0

    Re: Mitsubishi Electric air conditioner model : PUHY-200TEM-A

    hi,

    City Multi N/A Inverter IPM/bus over/under current detection, possible compressor fault, IPM damaged, disconnect compressor and measure inverter output all phase must be balan
    Mr Slim R410A power module, check compressor connections, mains voltage, compressor, power circuit board failure.