    Fujitsu asyg24lfcc



    Hello guy's, I fitted a new fujitsu wall mount in my local gym a couple of days ago. When I finished installing it, I gave it a good test run on heating and cooling, all seemed ok. A couple of days later, a proper electric supply was attached, just in time for busy spin class, should have been ok. Idiots down the gym fiddled with the remote, I showed them how to use it again, and again all seemed fine.
    I went down the gym this evening, as soon as I walked in, they started whingeing about the a/c not working, so I switched it back on, appeared to be fine. It seems to run for 15-20 mins the the indoor fan and compressor stops, louvres stay open, no sign of any fault codes.
    I have left it in that state, and will go back first thing in the morning to see if there is any codes or anything else obvious wrong.
    Any of you guys come across this before?



  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Fujitsu asyg24lfcc

    Hi Andy,

    No, not come across it before but i would make sure it hasn't reached its setpoint or defrosting or anything daft like that (guessing you have already done that though!) then have a look see if the room probe is reading correct - came across that once on a 2kW version come to think of it. Think on those the probe is soldered on the PCB.
    Health and safety first..........unless I'm in a hurry.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Fujitsu asyg24lfcc

    was it in heating mode as fan stops at setpoint

  4. #4
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Fujitsu asyg24lfcc

    Sheet of probe values me ol' china!
    Attached Files Attached Files
    Health and safety first..........unless I'm in a hurry.

  5. #5
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Fujitsu asyg24lfcc

    Definitely on cooling mode. I was thinking return sensor but surely the fan would still run regardless. The other thing I found strange was that when you start it in cooling, the fan won't go for at least 30 seconds.

  6. #6
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Fujitsu asyg24lfcc

    Cheers Tayters

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Fujitsu asyg24lfcc

    fan should start up as soon as louvres open, in cooling mode fan should run all the time in cooling mode
    http://www.mediafire.com/download/wk...ASYG12LECA.pdf
    closest service manual ive got

    Quote Originally Posted by Andy AC View Post
    Definitely on cooling mode. I was thinking return sensor but surely the fan would still run regardless. The other thing I found strange was that when you start it in cooling, the fan won't go for at least 30 seconds.

  8. #8
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: Fujitsu asyg24lfcc

    all I can add is "don't sh1t in your own garden".....lesson i learned long ago..

    Rule number one..any work you do for a local business/friend on the cheap WILL backfire.

  9. #9
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Fujitsu asyg24lfcc

    Cheers for that Monkey, Just been reading about your bad news, sorry to hear that mate. Hope your lucky pants work.

  10. #10
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Fujitsu asyg24lfcc

    Quote Originally Posted by eggs View Post
    all I can add is "don't sh1t in your own garden".....lesson i learned long ago..

    Rule number one..any work you do for a local business/friend on the cheap WILL backfire.
    Unfortunately where I am, everywhere is my back garden. And yes, the boss at the Gym is a friend

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Fujitsu asyg24lfcc

    no christmas card this year then if u dont fix it

    Quote Originally Posted by Andy AC View Post
    Unfortunately where I am, everywhere is my back garden. And yes, the boss at the Gym is a friend

  12. #12
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Fujitsu asyg24lfcc

    Return air probe appeared to be out, permanently attached to pcb . New board and probe to hopefully arrive Tuesday.
    Machine runs fine in test mode for 60 mins, which conveniently coincides with the duration of the spin classes, so I'm off the hook for a bit

  13. #13
    Join Date
    Jun 2010
    Location
    geraldton western australia
    Age
    39
    Posts
    57
    Rep Power
    14

    Re: Fujitsu asyg24lfcc

    Quote Originally Posted by Andy AC View Post
    Return air probe appeared to be out, permanently attached to pcb
    how do you confirm the thermistor is faulty if you cant disconnect it and test the resistance in isolation?

    did you meter it whilst it was still soldered to the pcb or did you chop it loose?

  14. #14
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Fujitsu asyg24lfcc

    Quote Originally Posted by assailant View Post
    how do you confirm the thermistor is faulty if you cant disconnect it and test the resistance in isolation?

    did you meter it whilst it was still soldered to the pcb or did you chop it loose?
    The data sheet has the voltage values at corresponding temperatures although a bit crazy to solder it in to begin with.
    Health and safety first..........unless I'm in a hurry.

  15. #15
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Fujitsu asyg24lfcc

    Had to measure it in place,not ideal I know. New board arrived late yesterday afternoon, fitted it even later last night and it don't work, new board faults straight away. 4 flash operation and 2 of timer. which I have believe is fault with emergency operation switch? Put original board back in, another board due friday.
    It was a crap end to an already crap day, previous job was changing a fan deck on a vaporex dehum in a hot swimming pool above a jacuzzi/spa. Apart from being drenched in sweat from head to toe, when finally switched on, it kept blowing rcd and mcb's. Whilst trying to find the fault, dropped my insulation tester in the spa. Turns out chlorinated water is not good for it.

  16. #16
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Fujitsu asyg24lfcc

    Quote Originally Posted by Andy AC View Post
    4 flash operation and 2 of timer. which I have believe is fault with emergency operation switch?
    Indoor coil probe error.
    Health and safety first..........unless I'm in a hurry.

  17. #17
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Fujitsu asyg24lfcc

    I didn't have a fujitsu manual handy, I used the troubleshooting guide in the climate center book. After dealing with that lot, no wonder they got the wrong code.
    With the new board, it faults immediately. I checked the coil thermistor reading the other day and it seemed fine.

  18. #18
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Fujitsu asyg24lfcc

    Fujitsu fault codes are at last standard if they are the G generation, as in ASYG.
    Not too sure what's in the NRS book but the last one i had didn't have this newer info, just the older stuff which to be fair was helpful - as long as it related to the unit you were working on. not that Fujitsu have made it easy with the fault codes in the first place.

    On that model the coil probe is plugged into fly lead coming off the PCB. Did that get missed out?

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  19. #19
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Fujitsu asyg24lfcc

    Thanks for the manual Andy. You were right the climate book did have the old info.
    I changed the board twice, just to make sure I didn't make any silly mistakes, still the same outcome.