    Question R-407C and Coil Capacity



    We've been using Colmac Coil's software for doing coil capacity estimates for system design. However, now we have a specification for designing a system using R-407C, a refrigerant that their coil software doesn't have available in its options.

    I know compressor capacity decreases a little bit with the change from R-22 to R-407C - at least the compressor manufacturers are up to date.

    Since I was unable to run a set of calculations for a coil for R-407C using the Colmac software, I decided to use Super Radiator Coil's software instead. Their software is a little less user friendly and also I don't have a lot of experience using it. However, when I put in R-22 numbers, and used the exact same numbers for R-407C, their software showed a slight increase in capacity for R-407C over R-22.

    Obviously there is an issue with high temperature ambient conditions because R-407C has a critical point about 86 deg C, whereas R-22 has a critical point about 100 deg. C. Therefore, there will obviously be a decrease in condenser capacity in R-407C at high outside temperatures.

    However, for normal air conditioning temperatures, say evaporator temperatures in the 5 deg C range and the ambient at the condenser at most about 45 deg. C, do the coils generally show an increase in capacity when going from R-22 to R-407C? I can see this happening due to the nature of the temperature glide in the coils, but my impression has been that if a unit is converted from R-22 to R-407C, generally there is a 5% to 7% decrease in capacity. Is this decrease in capacity based entirely on the decrease that comes at the compressor?



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: R-407C and Coil Capacity

    This makes for interesting reading and seems to answer your question. http://www.cnpam.edu.my/ICRAMME2005/...rs/PP/PP30.pdf

  3. #3
    Join Date
    Aug 2005
    Location
    Portland, Oregon, USA
    Posts
    18
    Rep Power
    0

    Re: R-407C and Coil Capacity

    "However, experimental data in association with this most important refrigerant substitute for R-22 are limited at the present time." and the report is dated May 2005. I suppose that is probably why Colmac hasn't added it to their software yet.

    Thanks very much.

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: R-407C and Coil Capacity

    R407c has been used in Europe since late 90s.
    Performance is 7% lower than R22 at the same working conditions, and SH, SC must be kept higher to prevent distillation of blend.

  5. #5
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Thumbs up Re: R-407C and Coil Capacity

    Ciat have some research on this subject.They did experiment with same chillers and diferent refrigerants.The R 407c have biger power consuption and small decrease in heat power.

    But use R22 calculator and calculate 5% decrease in heat power.

    Renato

  6. #6
    Join Date
    May 2006
    Location
    United Kingdom
    Age
    52
    Posts
    34
    Rep Power
    0

    Re: R-407C and Coil Capacity

    I think some manufacturers use either the dew or bubble point as design saturation temperature which can give capacitys higher or lower than R22. In practical terms you must use the bubble point & factor in 10k subcooling to ensure a good liquid seal in condensor. If not you'll get a breakdown of the refrigerant called fractionisation. My best advice is to avoid R407c as most manfacturers are switching to R134a on liquid chillers or other more stable refrigerants.