    Calculating compressor of a chiller



    Hi all.İ have a flow rate which is 3.6 m3/h

    İnlet water temperature:80 degrees of celcius
    outlet water temperrature:17 degrees of celcius

    Q = M x Cp X DT

    Q = Capacity in kW
    M = Liquid mass flow rate kg/s
    Cp = Liquid specific heat kJ/kg.K
    DT = Liquid temperature difference °C

    İ calculated and result is 264 kilo Joules.

    Can you verify this result?And can you help me find a compressor for this conditions?

    Thanks a lot



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Calculating compressor of a chiller

    Its 264 KW.
    It is correct.

  3. #3
    Join Date
    Sep 2013
    Location
    Turkey
    Age
    32
    Posts
    9
    Rep Power
    0

    Re: Calculating compressor of a chiller

    Thanks a lot chemi-cool

    This is very much heat capacity,isn't it?

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Calculating compressor of a chiller

    This is the heat you want to remove from the water to be cooled.

  5. #5
    Join Date
    Sep 2013
    Location
    Turkey
    Age
    32
    Posts
    9
    Rep Power
    0

    Re: Calculating compressor of a chiller

    Yes it is,i know.i need a compressor to remove that heat.How many horsepower should be?or kW

  6. #6
    Join Date
    Sep 2013
    Location
    Turkey
    Age
    32
    Posts
    9
    Rep Power
    0

    Re: Calculating compressor of a chiller

    Somebody help me please

  7. #7
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Calculating compressor of a chiller

    HP = 0.735KW

    Is your calculation a realistic idea?? 80 - 17 DegC
    I love the smell of Ammonia in the morning!

  8. #8
    Join Date
    Sep 2013
    Location
    Turkey
    Age
    32
    Posts
    9
    Rep Power
    0

    Re: Calculating compressor of a chiller

    İ know this HP = 0.735KW equation.

    The water reaches 80 degrees of celcius after using it.as far as I know

    So this is the important question:How big a compressor do i need for doing that?

  9. #9
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Calculating compressor of a chiller

    You need a big compressor and massive heat exchanger!!
    So before wasting time answering this question lets think realistically!

    Take your 80 degree leaving and put this through a dry cooler even in Turkey you can lower this 80 - 35 DegC with mechanical ventilation, add some evaporative cooling for better heat rejection!

    Now do your sums again with a delta T of 30 - 17

    I would check your original calculation as Cp for water at 80 DegC is 4.198 KJ/KgK
    Last edited by hookster; 18-09-2013 at 06:39 PM. Reason: Addittion as I did not read all post properly
    I love the smell of Ammonia in the morning!

  10. #10
    Join Date
    Sep 2013
    Location
    Turkey
    Age
    32
    Posts
    9
    Rep Power
    0

    Smile Re: Calculating compressor of a chiller

    i have 3.6 metriccube/h flow.

    This means mdot=1 kg/s -- C=4.180 kJ/kg.K --- deltaT=13 K

    Qdot(kJ/s)=mdot(kg/s)xC(kJ/kg.K)xdeltaT

    Qdot=54.4 kJ/second.

    So, is this the actual compressor size?or what?

    As you say i will use mechanical ventilation but i can obtain only 80>70 dCelcius.

    İ am mechanical engineering student.İ am new at this sector.As you can appreciate i need help.So i must say thanks for helping.

  11. #11
    Join Date
    Sep 2013
    Location
    Turkey
    Age
    32
    Posts
    9
    Rep Power
    0

    Re: Calculating compressor of a chiller

    Quote Originally Posted by hookster View Post

    I would check your original calculation as Cp for water at 80 DegC is 4.198 KJ/KgK
    Is this important?I took it as average.I guess