    Versatemps



    Hi,
    Has anyone any information on versatemp fault codes, ideally the meaning behind F1 & F2 codes on model types VM2/S & VM3 (old systems running on R22)

    Thanks



  2. #2
    justchill's Avatar
    justchill Guest

    Re: Versatemps

    F1 is high pressure F2 is water temp out of range

  3. #3
    Join Date
    Nov 2005
    Location
    england
    Posts
    2
    Rep Power
    0

    Re: Versatemps

    Spot on, thanks for the info

  4. #4
    Join Date
    Aug 2002
    Location
    Lancashire
    Age
    71
    Posts
    8
    Rep Power
    0

    Re: Versatemps

    Hi all,
    Talking about Versatemp. units. We are looking after many versatemp. units in a large building. What puzzles me is that we can have two units next to each other, on the same cond. water line at the same temp. but each unit has a different cooling/ heating capacity.
    Gas charge is OK in both units, comps seems OK. Running amps OK, pressures the same on each unit.
    Any one got experience with these units and can give any advise as to why they are different ?
    cheers.

  5. #5
    rbartlett's Avatar
    rbartlett Guest

    Re: Versatemps

    Quote Originally Posted by reefer
    Hi all,
    Talking about Versatemp. units. We are looking after many versatemp. units in a large building. What puzzles me is that we can have two units next to each other, on the same cond. water line at the same temp. but each unit has a different cooling/ heating capacity.
    Gas charge is OK in both units, comps seems OK. Running amps OK, pressures the same on each unit.
    Any one got experience with these units and can give any advise as to why they are different ?
    cheers.
    different size units? How are you measuring this difference ??

    post more info model no/s rating, compressor amps etc

    I have done many versatemps systems over the years and most problems are water (flow) related..

    cheers

    richard

  6. #6
    Join Date
    Aug 2002
    Location
    Lancashire
    Age
    71
    Posts
    8
    Rep Power
    0

    Re: Versatemps

    Hi Richard,
    Thanks for the reply.
    I will get the info and post it as soon as I can,
    cheers,
    Alan

  7. #7
    Join Date
    Aug 2002
    Location
    Lancashire
    Age
    71
    Posts
    8
    Rep Power
    0

    Re: Versatemps

    Here is some data from these units,
    model EQV2024 R22
    inlet water 23.9C
    outlet water 26.8C
    comp. amps 2.8 / 3A
    dish. 165psig
    suct 73psig
    cooling mode
    condenser water is 2 pipe system with temp. control from pump room.

    all units are the same model, made in 1995.
    thanks,
    reefer

  8. #8
    rbartlett's Avatar
    rbartlett Guest

    Re: Versatemps

    on those figures I would check the compressor for pumping efficiency

    73 psig on R22 means an evaporating pressure of 7 deg's C

    I would look for 60ish psig on the suction and 200+ on the discharge

    and I think the running amps should be nearer 6-10 if it's a 24k btu

    cheers

    richard
    Last edited by rbartlett; 31-03-2006 at 03:58 PM.

  9. #9
    Join Date
    Aug 2002
    Location
    Lancashire
    Age
    71
    Posts
    8
    Rep Power
    0

    Re: Versatemps

    Hi Richard,
    Sorry for the very late reply, work etc got in the way.
    Thanks for your advise on the versatemps. Will check them out next we visit the site,
    reefer