    ECM evap motors running backwards after a power surge.?



    We've been using Wellington ECM fan motors for a while now with no issues. Now a customer calls a claims that if there is a power surge his meat case fans reverse themselves. Has anyone had issues of this nature with this type of fan? Is it even possible. Mfr. says no but Just putting it out there. Thanks, Ken



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: ECM evap motors running backwards after a power surge.?

    Are they DC?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: ECM evap motors running backwards after a power surge.?

    Do they all reverse or just some of them?

    If just some then perhaps they are just not running but being spun by the airflow of the ones that are running.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Dec 2005
    Location
    USA
    Posts
    222
    Rep Power
    20

    Re: ECM evap motors running backwards after a power surge.?

    Well thanks for the replies. let you know when i find some new evidence. Phones been quiet today. LOL.Ken

  5. #5
    Join Date
    Aug 2013
    Location
    Portugal
    Posts
    20
    Rep Power
    0

    Re: ECM evap motors running backwards after a power surge.?

    Quote Originally Posted by Brian_UK View Post
    Do they all reverse or just some of them?

    If just some then perhaps they are just not running but being spun by the airflow of the ones that are running.
    Even so they should turn around in the same direction, not in reverse...
    I suppose they can run in reverse if someone changed some conections...

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: ECM evap motors running backwards after a power surge.?

    Hi, TERRENAS

    Quote Originally Posted by TERRENAS View Post
    Even so they should turn around in the same direction, not in reverse...
    I suppose they can run in reverse if someone changed some conections...
    You are quite sure?

    I'm

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: ECM evap motors running backwards after a power surge.?

    not too up on electrics,but had a 3 phase cond motor do it my mate who is more up to speed said it was known as ghosting,way beyond me i just treat elctrickery with the utmost respect.

  8. #8
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: ECM evap motors running backwards after a power surge.?

    Quote Originally Posted by cadwaladr View Post
    not too up on electrics,but had a 3 phase cond motor do it my mate who is more up to speed said it was known as ghosting,way beyond me i just treat elctrickery with the utmost respect.
    I was on the opinion as with the other posts about client issue but cadwaladr got me thinking about "ghosting" or stray voltage and with an ECM fan depending on wiring of course the possibility that the fan controller sees stray voltage via its PWM input which if it was earth leakage would be more negative to reference. I do not think it is impossible to commutate a synchronous motor in the reverse direction as manufacturer states.

    Maybe try improve earthing arrangment or voltage regulation to fan controller.
    I love the smell of Ammonia in the morning!

  9. #9
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: ECM evap motors running backwards after a power surge.?

    Hi Terrenas
    Brian is correct.
    When there are multiple fans on and evap and one fails the others will suck air in through this fan (air will take path of least resistance) and because the airflow is reversed the direction of rotation of the fan will be reversed.
    This has caught out a lot of inexperienced people and will continue to do so i would suggest.
    Regards
    Paul

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: ECM evap motors running backwards after a power surge.?

    Here is description from Welington:
    ECM Technology

    Types of electric motor differ largely in how they achieve the interaction of magnetic fields, and most importantly the field reversals, necessary to make the motor turn. Electronically commutated (ECM) motors are brushless DC motors where the direction of the electric current is switched using electronic controllers. As the switching of the current is technically known as "commutating”, brushless motors are also called “electronically commutated” motors.
    I would say yes, it is highly possible that power surge makes electronic circuitry to change direction of fan rotation.
    Last edited by nike123; 20-09-2013 at 06:46 AM.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: ECM evap motors running backwards after a power surge.?

    Quote Originally Posted by chemi-cool View Post
    Are they DC?
    Yes they are!


  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: ECM evap motors running backwards after a power surge.?

    Second part:

  13. #13
    Join Date
    Jul 2013
    Location
    USA
    Posts
    58
    Rep Power
    11

    Re: ECM evap motors running backwards after a power surge.?

    Try adding some capacitors to the power supply rails.

    Modern inverter drive ("ECM" or "brushless DC") motors are very sophisticated inside. Many modern implementations, such as Delta's Cindy Wu sensorless FOC (used mostly for cooling high performance computers), dispense with the resolver altogether and replace it with a single chip computer to derive the rotor position and hold the stator flux 90 electrical degrees ahead of the rotor, where the efficiency is the best.

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: ECM evap motors running backwards after a power surge.?

    Rotation Sensing


    The first time the Evergreen EM is powered up and receives a signal on
    one of the Low Voltage Signal terminals, it will perform a Rotation Sensing
    process. With this feature, the motor will automatically determine the proper
    operating direction of the blower wheel by running the motor for several
    seconds in each direction.
    Do not turn off the “High Voltage Power” or the “Low Voltage Signal inputs”
    to the motor until the motor continues to run in one direction. During Rotation
    Sensing, the motor will run in both directions, up to four times if necessary, to
    determine the proper operating direction. If the proper direction cannot be
    determined after the forth sequence, the motor will operate in the default
    direction of counter clock-wise (CCW).
    Once the motor continues to run in one direction, Rotation Sensing is complete
    and the feature is locked out. The motor will continue to start and run in this direction
    without performing Rotation Sensing even if the High Voltage Power is disconnected.
    If the final operating direction of the motor is not the proper direction for the
    blower wheel, go to the “Troubleshooting Guidelines” on page 14; “Wrong
    Rotation”.

    Page 11 here:
    http://www.mediafire.com/?l75am5wahwvjkqw

  15. #15
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: ECM evap motors running backwards after a power surge.?

    Thanks Nike.
    Brilliant!
    Grizzly

  16. #16
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: ECM evap motors running backwards after a power surge.?

    Quote Originally Posted by nike123 View Post
    Rotation Sensing


    The first time the Evergreen EM is powered up and receives a signal on

    Snip

    motor is not the proper direction for the
    blower wheel, go to the “Troubleshooting Guidelines” on page 14; “Wrong
    Rotation”.

    Page 11 here:
    http://www.mediafire.com/?l75am5wahwvjkqw

    As usual excellent information.