  1. #1
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    High Discharge Temperature!!! Very Critical



    Hey friends

    I am on a site where we have J&E hall Screw Compressor we do some Retrofit with chiller,And add only 40kg Gas R22(But Labeled 70Kg) and started MAchine. But Machine going in very high discharge Temperature.Which is not good for compressor Life.Below are the parameters for the same.Please Suggest What is wrong.Its a 4 circuit Chiller.


    For refrence I am attaching Log in form of Image.
    Attached Images Attached Images
    • File Type: jpg 1.JPG (74.8 KB, 299 views)
    Last edited by MayankBhatia; 17-09-2013 at 05:14 PM. Reason: Full details with Amps and actual temp



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: High Discharge Temperature!!! Very Critical

    What type of condenser do you have fitted?

    Was a good vacuum achieved before regassing?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,094
    Rep Power
    23

    Re: High Discharge Temperature!!! Very Critical

    What are your water in/out temps? Is this just after initial pull down of load. Just wondering if there was too much load on pull down, not that I know much about screws. Please include ambient temp and humidity too.
    Why not visit my website: www.rockncrystals.com.au ?

  4. #4
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    Re: High Discharge Temperature!!! Very Critical

    Condenser is Air Cooled.and yes we achieved 400 Micron in all circuts.

    OAT: 42 °C Set Point:5.5 °C EWT: 11.6°C LWT: 6.1°C

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: High Discharge Temperature!!! Very Critical

    High oil temps and or low flow rates will effect discharge temps.

  6. #6
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: High Discharge Temperature!!! Very Critical

    What is the chiller model No. and you said only charged 40 kg from total charged 70 kg gas. Then you have got the temperature entering and leaving is 11 and 6!! .be sure it is correct, and your suction super heat is not much high. Considering the all readings your gas charging is full and sufficient. What are the full load compressor amps to compare RLA. Restricted oil flow to the compressor will cause high discharge temperature. Check for main injection valve, oil orifice or filter blockage. Has your compressor oil cooling system?

  7. #7
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    337
    Rep Power
    21

    Re: High Discharge Temperature!!! Very Critical

    Looking at the condensing pressures & outside air temperatures - those discharge temperatures are probably to be expected..

  8. #8
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    254
    Blog Entries
    4
    Rep Power
    20

    Re: High Discharge Temperature!!! Very Critical

    I am thinking the same thing! You can make improvements but I would except higher than normal discharge temperatures. What is your cutout point? 120c?

  9. #9
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by Magoo View Post
    High oil temps and or low flow rates will effect discharge temps.
    High Oil temperature?But what making oil Temp High.?At the start of Compressor at full load it shows 29 DSH but slowly slowly Discharge temp Increases.

    And Can you little explain How flow Rate Will Effect?

  10. #10
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by moideen View Post
    What is the chiller model No. and you said only charged 40 kg from total charged 70 kg gas. Then you have got the temperature entering and leaving is 11 and 6!! .be sure it is correct, and your suction super heat is not much high. Considering the all readings your gas charging is full and sufficient. What are the full load compressor amps to compare RLA. Restricted oil flow to the compressor will cause high discharge temperature. Check for main injection valve, oil orifice or filter blockage. Has your compressor oil cooling system?
    Its a Mcquay ALS Chiller.FLA was 160 Amps.

  11. #11
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by passandscore View Post
    I am thinking the same thing! You can make improvements but I would except higher than normal discharge temperatures. What is your cutout point? 120c?
    Cut point for Discharge temperature is 110 degree Celcius.

  12. #12
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: High Discharge Temperature!!! Very Critical

    Hi, MayankBhatia

    Quote Originally Posted by MayankBhatia View Post
    Hey friends

    I am on a site where we have J&E hall Screw Compressor we do some Retrofit with chiller,And add only 40kg Gas R22(But Labeled 70Kg) and started MAchine. But Machine going in very high discharge Temperature.Which is not good for compressor Life.Below are the parameters for the same.Please Suggest What is wrong.Its a 4 circuit Chiller.


    For refrence I am attaching Log in form of Image.
    I have to admit have no experience with J&E Hall screws, but ... compressor like compressor or almost the same ...

    discharge temp in single stage screw compressor for ammonia can go up to 105*C but with R 22 only up to 90*C ... maybe with air cooled condensers those value are higher ... anyhow problem is within oil temperature for bearings ... must not be over 75*C ...

    seems your discharge temp is very high ... what is cause ....

    suction superheat is quite low (what is good) ....

    discharge superheat is very high, too high .. above 25K ... you have 36,3 to 39,5 K

    oil pressure difference is OK from 0,7 to 1,0 bar ... permissible oil drop pressure can be max about 1,75 bar (0,35 bar g for clean filter + 1,4 bar)

    seems your liquid refrigerant injection for oil cooling is not enough (I assume you start up your plant sometime in the winter period thus you did not have the same OAT like now ...maybe I'm wrong) thus you need to install small external oil cooler for additional oil cooling... no other way, sorry ...

    with refrigerant injection for oil cooling discharge temperature above 75*C is not possible to maintain .... in your case discharge temperature are from 99,8 to 104,9*C (oil has the same temperature)

    Hope this will be of some help to you.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  13. #13
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by Josip View Post
    Hi, MayankBhatia



    I have to admit have no experience with J&E Hall screws, but ... compressor like compressor or almost the same ...

    discharge temp in single stage screw compressor for ammonia can go up to 105*C but with R 22 only up to 90*C ... maybe with air cooled condensers those value are higher ... anyhow problem is within oil temperature for bearings ... must not be over 75*C ...

    seems your discharge temp is very high ... what is cause ....

    suction superheat is quite low (what is good) ....

    discharge superheat is very high, too high .. above 25K ... you have 36,3 to 39,5 K

    oil pressure difference is OK from 0,7 to 1,0 bar ... permissible oil drop pressure can be max about 1,75 bar (0,35 bar g for clean filter + 1,4 bar)

    seems your liquid refrigerant injection for oil cooling is not enough (I assume you start up your plant sometime in the winter period thus you did not have the same OAT like now ...maybe I'm wrong) thus you need to install small external oil cooler for additional oil cooling... no other way, sorry ...

    with refrigerant injection for oil cooling discharge temperature above 75*C is not possible to maintain .... in your case discharge temperature are from 99,8 to 104,9*C (oil has the same temperature)

    Hope this will be of some help to you.

    Best regards, Josip
    Do you mean i need to Increase orifice of Liquid injection?

  14. #14
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: High Discharge Temperature!!! Very Critical

    Hi, MayankBhatia

    Quote Originally Posted by MayankBhatia View Post
    Do you mean i need to Increase orifice of Liquid injection?

    Actually no ... it is not allowed to you to alternate injection ports ... not your job ... it is installed by manufacturer to protect compressor ...

    but, you can try, there is a big danger to have too much refrigerant within oil i.e. lack of lubrication what is not good either ...

    ... anyhow you can try to increase amount of injected refrigerant for oil cooling, but ... do it carefully and check oil pressure and discharge temperature ... and if need install additional external oil cooler ...

    Did you check you liquid refrigerant line ... to injection port ... no lack of refrigerant in that line-pipe ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  15. #15
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: High Discharge Temperature!!! Very Critical

    MayankBhatia,
    What type of oil cooling do you have, as I can't find it in any of your above posts!

    I have seen in one case with liquid injection that refrigerant injection tubes entering slide valves were worn & nearly all liquid leaked into suction & star wheel chamber. Maybe this is not relevant but worth mentioning.

    Also how old are these compressors & have they performed with lower discharge temps in the past.

    Discharge pressures seem excessive in all systems even for ambient of 42 C
    From what I can find max dt 100C normal comp & 120C special max oil temp 80C
    Max dp 27bar with it being on border of using liquid injection cooling.
    Last edited by RANGER1; 17-09-2013 at 10:13 PM.

  16. #16
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by RANGER1 View Post
    MayankBhatia,
    What type of oil cooling do you have, as I can't find it in any of your above posts!

    I have seen in one case with liquid injection that refrigerant injection tubes entering slide valves were worn & nearly all liquid leaked into suction & star wheel chamber. Maybe this is not relevant but worth mentioning.

    Also how old are these compressors & have they performed with lower discharge temps in the past.

    Discharge pressures seem excessive in all systems even for ambient of 42 C
    From what I can find max dt 100C normal comp & 120C special max oil temp 80C
    Max dp 27bar with it being on border of using liquid injection cooling.
    Compressors are Just brand New,as I told We retrofitted it.Oil is refregerant cooled.Its J&E Hall HSS Series3100 Compressor.

  17. #17
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by MayankBhatia View Post
    Compressors are Just brand New,as I told We retrofitted it.Oil is refregerant cooled.Its J&E Hall HSS Series3100 Compressor.
    hi mayan

    again let me confirm,you replaced only compressor.may i know before which compressor was used.is it same Mcquay?and give me chiller full model no.

    regards
    moideen-dubai

  18. #18
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    Re: High Discharge Temperature!!! Very Critical

    Yes it was Same Mcquay Screw Compressor, ALS294A.Please help?Could it be related to Flow anyhow?

  19. #19
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: High Discharge Temperature!!! Very Critical

    Yes mayan, for screw compressors oil has multipurpose. Such
    as lubrication, sealing of gas leakage and reducing the discharge temperature. And also your chiller has equipped with liquid injection. So you have to check two main things. Check the oil temperature, any restriction in oil flow and the liquid injection is working properly.

  20. #20
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by moideen View Post
    Yes mayan, for screw compressors oil has multipurpose. Such
    as lubrication, sealing of gas leakage and reducing the discharge temperature. And also your chiller has equipped with liquid injection. So you have to check two main things. Check the oil temperature, any restriction in oil flow and the liquid injection is working properly.
    The oil Temp is same as Discharge Temp.And Liquid Injection is working Fine.

    And With flow mean Water Flow,As i am having only 3 PSi Pressure Drop across Evaporator.

  21. #21
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: High Discharge Temperature!!! Very Critical

    Oil & discharge temp should be 90deg C so either liquid injection is not quite working 100% lack of refrigerant or needs adjustment

    http://www.jehall.com/library/docs/h...-2.3-07-11.pdf

    You may have information like this with new machines?
    Last edited by RANGER1; 18-09-2013 at 09:29 PM.

  22. #22
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by RANGER1 View Post
    Oil & discharge temp should be 90deg C so either liquid injection is not quite working 100% lack of refrigerant or needs adjustment

    http://www.jehall.com/library/docs/h...-2.3-07-11.pdf

    You may have information like this with new machines?
    Yes i am aware of that.I have set Liquid Injection solenoid coil to energize at 80 degree .And System doesnt show any sign of lack of refrigerant like Sub cooling is fine and Sight glass also clear.

  23. #23
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: High Discharge Temperature!!! Very Critical

    Too high a pressure of condensation. Motor winding give much more heat, well it turns out DSH above norms.
    For r-22 30-35 K OK

  24. #24
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: High Discharge Temperature!!! Very Critical

    As RusBuka mentioned, too high condensation temperature (for that ambient temperature) is on these records. Compressors are overloaded. High discharge temperature is result of that overload. Condenser split (TD) is 21,5K to 23K (according to records) which is excessive to me. I would expect, in that climate, to use high efficiency condensers with split of 10K, no more! What if ambient temperature go higher?

    So I will be first checking if condenser is clean, fans are rotating in right direction and at proper rpm-s. If you have condensation control, than I would try to run fans at full speed with bypassing condensation control circuit. If you have condenser air-flow design data, then it is best to measure actual condenser air flow.
    I would expect there to have condensers with at least 300m3/h air flow per 1kW of chiller cooling capacity.
    I am not pulling these numbers from my head. They are numbers from technical data of McQuay chillers ALS “E” XE ST (HFC 134a)

    http://www.mcquay.ru/downloads/ALS%20E_tm_en.pdf

    XE in designation means that it is high efficiency heat exchanger (condenser) which is able to run up to 48°C ambient temperature, which should be used in your area.


    Also, these data will let you know if it is problem with design (to small condenser) or with function of condenser.
    To me, in this case, condenser is starting point.

    Also, I would measure condenser air exit temperature to be able to calculate condenser approach!

    When you lower that split to 10K-12K, I expect you will have no more problems with high DSH, if everything else is OK.
    Last edited by nike123; 19-09-2013 at 08:51 AM.

  25. #25
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: High Discharge Temperature!!! Very Critical

    How certain is the OP that the refrigerant provided is in fact R22?

    Certain Chinese blends - marked as R22 - can create all kinds of havoc in a system. I've seen this with refrigerant marked R134a, for instance. The difference in performance figures between DuPont R134a & Chinese 'R134a' is shocking!
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  26. #26
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by nike123 View Post
    As RusBuka mentioned, too high condensation temperature (for that ambient temperature) is on these records. Compressors are overloaded. High discharge temperature is result of that overload. Condenser split (TD) is 21,5K to 23K (according to records) which is excessive to me. I would expect, in that climate, to use high efficiency condensers with split of 10K, no more! What if ambient temperature go higher?

    So I will be first checking if condenser is clean, fans are rotating in right direction and at proper rpm-s. If you have condensation control, than I would try to run fans at full speed with bypassing condensation control circuit. If you have condenser air-flow design data, then it is best to measure actual condenser air flow.
    I would expect there to have condensers with at least 300m3/h air flow per 1kW of chiller cooling capacity.
    I am not pulling these numbers from my head. They are numbers from technical data of McQuay chillers ALS “E” XE ST (HFC 134a)

    http://www.mcquay.ru/downloads/ALS%20E_tm_en.pdf

    XE in designation means that it is high efficiency heat exchanger (condenser) which is able to run up to 48°C ambient temperature, which should be used in your area.


    Also, these data will let you know if it is problem with design (to small condenser) or with function of condenser.
    To me, in this case, condenser is starting point.

    Also, I would measure condenser air exit temperature to be able to calculate condenser approach!

    When you lower that split to 10K-12K, I expect you will have no more problems with high DSH, if everything else is OK.
    hi, nike .your observations are correct to me. Yes td is high. But in hot climate in dubai used td is maximum 17k.so the maximum condensing temperature should reach to 59c(331psig) at 42 ambient. Here discharge is high and check the subcooling is 12.therefore reducing gas charge to 8k sub cooling, can control discharge pressure and bring back the compressor amps to below compressor RLA 160 Amps. mayan Bhatia has to provide the readings of air entering and leaving temperature.

  27. #27
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: High Discharge Temperature!!! Very Critical

    Place the liquid receiver. Fill up To 2-3 subcool.
    Without economizer does not make sense.

  28. #28
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by nike123 View Post
    As RusBuka mentioned, too high condensation temperature (for that ambient temperature) is on these records. Compressors are overloaded. High discharge temperature is result of that overload. Condenser split (TD) is 21,5K to 23K (according to records) which is excessive to me. I would expect, in that climate, to use high efficiency condensers with split of 10K, no more! What if ambient temperature go higher?

    So I will be first checking if condenser is clean, fans are rotating in right direction and at proper rpm-s. If you have condensation control, than I would try to run fans at full speed with bypassing condensation control circuit. If you have condenser air-flow design data, then it is best to measure actual condenser air flow.
    I would expect there to have condensers with at least 300m3/h air flow per 1kW of chiller cooling capacity.
    I am not pulling these numbers from my head. They are numbers from technical data of McQuay chillers ALS “E” XE ST (HFC 134a)

    http://www.mcquay.ru/downloads/ALS%20E_tm_en.pdf

    XE in designation means that it is high efficiency heat exchanger (condenser) which is able to run up to 48°C ambient temperature, which should be used in your area.


    Also, these data will let you know if it is problem with design (to small condenser) or with function of condenser.
    To me, in this case, condenser is starting point.

    Also, I would measure condenser air exit temperature to be able to calculate condenser approach!

    When you lower that split to 10K-12K, I expect you will have no more problems with high DSH, if everything else is OK.

    Thanks Nike for your detailed Observation.Condenser air Inlet and Outlet Difference is About 20-25Degree Celcius.

    And is Condenser Split the same as of difference bw Condenser air and Out Temp?

  29. #29
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by moideen View Post
    hi, nike .your observations are correct to me. Yes td is high. But in hot climate in dubai used td is maximum 17k.so the maximum condensing temperature should reach to 59c(331psig) at 42 ambient. Here discharge is high and check the subcooling is 12.therefore reducing gas charge to 8k sub cooling, can control discharge pressure and bring back the compressor amps to below compressor RLA 160 Amps. mayan Bhatia has to provide the readings of air entering and leaving temperature.
    i also Tried Taking out Some GAs From System so to have Subcooling Near about 8 but still no more effect.
    But the thing is the refregeerant which need to be charge i didnot charge that much.as on name plate we should charge approx 70Kg but i charge near 40 Kg.

  30. #30
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: High Discharge Temperature!!! Very Critical

    Can you post photo of info about chiller?

  31. #31
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by MayankBhatia View Post
    Thanks Nike for your detailed Observation.Condenser air Inlet and Outlet Difference is About 20-25Degree Celcius.

    And is Condenser Split the same as of difference bw Condenser air and Out Temp?
    25c is very high. It is tell us very clearly the air flow is not sufficient. No test is valid if the air flow is not correct. The condenser air delta temperature has to bring to the level of between 8c to10c

  32. #32
    Join Date
    Dec 2012
    Location
    Dubai
    Posts
    42
    Rep Power
    0

    Re: High Discharge Temperature!!! Very Critical

    Quote Originally Posted by moideen View Post
    25c is very high. It is tell us very clearly the air flow is not sufficient. No test is valid if the air flow is not correct. The condenser air delta temperature has to bring to the level of between 8c to10c
    Ok I will Measure the Air Flow and will revert. 1 thing what is correct method of measuring Air Flow in Air cooled Condenser? I mean i have Aneemometer i should place it near tip of fan then measure its velocity?
    Last edited by MayankBhatia; 20-09-2013 at 02:35 PM.

  33. #33
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: High Discharge Temperature!!! Very Critical

    Measure the size of the condenser coil face and use your anemometer on the coil face.
    Brian - Newton Abbot, Devon, UK