    Exclamation rotory compressor gone under vaccum while working



    hai gents,
    i am attending one complaint of mitsubishi mr:slim air conditioning unit.after starting its suction gone in to vaccum.this compressor also new.



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: rotory compressor gone under vaccum while working

    Quote Originally Posted by prijorobert View Post
    hai gents,
    i am attending one complaint of mitsubishi mr:slim air conditioning unit.after starting its suction gone in to vaccum.this compressor also new.
    Hi, prijrobert, welcome to re.First ensures the system has charged sufficient refrigerant. If there is no gas, it required leak test and related job. If it is normal, then check the blockage of refrigerant through the circuit such as liquid line drier and expansion valve, also check any service valves whether it is closed.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: rotory compressor gone under vaccum while working

    ask the company who fitted it if he had a vac pump??
    as moideen says- check standing pressure see if theres any gas in it, u need to determine if it was sufficiently charged and proove theres no leak on the system, finally if the strainer gauzes are blocked

  4. #4
    Join Date
    Sep 2013
    Location
    Turkey
    Age
    32
    Posts
    9
    Rep Power
    0

    Re: rotory compressor gone under vaccum while working

    Quote Originally Posted by prijorobert View Post
    hai gents,
    i am attending one complaint of mitsubishi mr:slim air conditioning unit.after starting its suction gone in to vaccum.this compressor also new.
    As moideen said,check the circuit.İf circuit is old,%80 circuit is filled up with refrigerant oil.Please change your circuit with new one.