    Bluebox chiller fault



    Hi I have a blue box chiller model-KAPPA.V/LN 37.2 serial BBOX010139 it is showing a protectioner load fault and can't be reset via the carel controller. I have checked motor controller all hp switch compressor thermistors does anyone know what this fault means. A wiring diagram would also help



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Bluebox chiller fault

    I've never come across that fault and can't find any reference to it.
    Maybe call their technical number?

    +39 0426 921 111
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Bluebox chiller fault

    Hi Mikas.
    A stupid question maybe!
    But have you checked the Incoming supplies and contactors?
    Worth a try.
    Grizzly

  4. #4
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Bluebox chiller fault

    Hi Mikas

    This sounds like it is the electronic motor protection unit fault for the compressor. The motor protection module can be reset by removing the power feed to it for 25s. It stores fault counts then locks out till reset.
    If it does not reset or resets then faults again you either have motor motor thermo protection fault or faultly compressor motor.
    You are unable to reset this from controller.
    I love the smell of Ammonia in the morning!