    Hi all,

    I'm going to be installing a twin split system soon (mitsubishi elec), I'd just like to know if anyone has any details or links to any manuals with regards to master and slave settings and measurements from refnets etc so I can get a bit of a head start! Any info much appreciated as always!

    Thanks in advance

    CraigF



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi twin splits.

    refnet equal distance between 2 indoors
    s1 s2 s3 to both indoors
    remote controller to 1 indoor only- no addressin as its classed as a single split
    Last edited by install monkey; 11-09-2013 at 09:54 PM. Reason: deffo a mitsi- as another thread took over 47 posts to discover its a blue machine! haha

  3. #3
    Join Date
    Dec 2011
    Location
    England
    Age
    42
    Posts
    131
    Rep Power
    14

    Re: Mitsubishi twin splits.

    Seems pretty simple stuff then! Cheers!

  4. #4
    Join Date
    Dec 2011
    Location
    England
    Age
    42
    Posts
    131
    Rep Power
    14

    Re: Mitsubishi twin splits.

    S123 two separate cables from outdoor?

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi twin splits.

    all 410a mr slims 7-14kw 5/8 3/8 pipe and from each branch if 2x 5kw its 1/2 an 1/4- or 5/8 3/8 for 7 kw indoors
    additional charge is based on total length of main run and the 2 branches

  6. #6
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Mitsubishi twin splits.

    Quote Originally Posted by CraigF View Post
    S123 two separate cables from outdoor?
    one cable a 4 core cable, usually use 1.5mm or 2.5mm 4 core sy cable.
    S1 is live
    S2 Neutral
    S3 Comms
    Earth to Earth terminal.

    hope this helps

  7. #7
    Join Date
    Dec 2011
    Location
    England
    Age
    42
    Posts
    131
    Rep Power
    14

    Re: Mitsubishi twin splits.

    Spot on mate! Am I cabling s1s2s3 in separate 1.5mm from outdoor unit or will that be daisy chain from one to the other? Sorry I'm a simpleton!

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi twin splits.

    outdoor to 1st/nearest unit then out on the same terminals to the slave unit

  9. #9
    Join Date
    Dec 2011
    Location
    England
    Age
    42
    Posts
    131
    Rep Power
    14

    Re: Mitsubishi twin splits.

    Cheers moondawn as i was more thinking along the lines of an individual 1.5mm four core for each indoor from the outdoor unit mate.

  10. #10
    Join Date
    Dec 2011
    Location
    England
    Age
    42
    Posts
    131
    Rep Power
    14

    Re: Mitsubishi twin splits.

    Cheers install! Cheers moondawn!

  11. #11
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Mitsubishi twin splits.

    Quote Originally Posted by CraigF View Post
    Cheers moondawn as i was more thinking along the lines of an individual 1.5mm four core for each indoor from the outdoor unit mate.
    Hi yeah one cable from outdoor condensor daisy chained through the indoors.
    Beat me to it monkey

  12. #12
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Mitsubishi twin splits.

    Indoor that you connect the controller to becomes the master.
    Standard configuration will take an average temperature from both indoor units return air to achieve your set temp.
    This can also be changed via the PAR-30/31 to: (function setting mode 02)
    Temp sensor to which the controller is connected to. (master indoor)
    Temp sensor built into the controller.

    Distance between refnet and indoors can be (iirc) 8m difference max between the two lengths but always good practice to keep them equal as IM said above. (check the manual that comes in the refnet box, not the indoor manual)


  13. #13
    Join Date
    Dec 2011
    Location
    England
    Age
    42
    Posts
    131
    Rep Power
    14

    Re: Mitsubishi twin splits.

    Thanks slim!