26-02-2006, 10:20 PM #1
Blast freezer temperature problem. Please help!!!
I have a blast freezer with Bitzer S6F-30.2Y compressor. It normally goes down to -35c with 1.2 ton of fish in 8 hours. After service by an unqualified technician, it now takes 14 hours to reach -14c.
Parameters are:
18.5Amp
Discharge=224psi
Suction=8psi
Intermediate Pressure=89psi
Superheat bulb temp=34.7c
Oil pressure=94psi
I also have a little ice on the suction cup at the entrance to the cylinder, but not on the cylinder head.
I need help getting the system back to normal. Do I need to adjust the superheat or is it something else?
Any help will be appreciated. Thanks.
-
26-02-2006, 10:29 PM #2
Re: Blast freezer temperature problem. Please help!!!
Hi Volta
you seem to know more than the average owner
Not a fridge guy in disguise
If your bulb temperature you refer to is the bulb for the evaporator your plant has 60k super heat, should be say 20k at the compressor inlet, depending on the suction pipe length.
Why not get the guy who installed it back to put it right, or have you not paid him
Evaporator is being starved of refrigerant, short of gas, blockage somewhere or incorrectly set expansion valve.
Kind Regards. Andy.
-
26-02-2006, 10:41 PM #3
Re: Blast freezer temperature problem. Please help!!!
Thanks Andy,
The bulb I was referring to is the superheat bulb.
We just reloaded the system with 124kg of R507, which is the correct amount for this system.
I already changed the evaporator TXV with a new one with the same orifice.
I still have the same problem. Any ideas?
I can't get a real qualified tech since my equipment is in Africa.
-
26-02-2006, 11:23 PM #4
Re: Blast freezer temperature problem. Please help!!!
Originally Posted by volta
cheers
richard
-
26-02-2006, 11:54 PM #5
Re: Blast freezer temperature problem. Please help!!!
Don't panic Rich, it'll be OK.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
27-02-2006, 09:22 AM #6
Re: Blast freezer temperature problem. Please help!!!
Originally Posted by volta
to adjust tev ,,you must check the p-t chart of gas 507
you can find this chart at:
www.refrigerants.com/pics/ptchart.pdf
if you need a blast temp. -35 , the evaporator temp. will be -38 , and with 5 dgree superheat it will match -33
this temp. match pressur 10 psi
so you must increase the orifice of tev by rotate it clock wise untill you get 10 psi suction pressure
an other reason you check is:
may be the evaporator coil may be dirty,,alot of impurities stucking on its surface,,so it must be cleaned away ,
thats all i have to tell you
good luck
afeef
-
27-02-2006, 11:01 AM #7
Re: Blast freezer temperature problem. Please help!!!
I can't get a real qualified tech since my equipment is in Africa
and 18.5 amp ?? what is that? if its the comp. running current the it sounds very low for the plant. suspect poor duty due to some kind of restriction if you are sure the charge is correct.Last edited by slingblade; 27-02-2006 at 11:08 AM.
Takes a licking, keeps on ticking.
-
27-02-2006, 11:18 PM #8
Re: Blast freezer temperature problem. Please help!!!
Originally Posted by volta
Did you set the TXV superheat, open the valve adjust screw out until the superheat lowers to 10k at evaporator outlet, you may then proceed to play with it until you get a 4.5k superheat, but I wouldn't bother.
Fit a pressure gauge and a thermometer probe at the evaporator outlet. Read off the saturation pressure and convert to degrees c for the refrigerant used. Then adjust the valve until the probe reads within 10K of the pressure reading in Deg C.
Then retire to the pub and tell your mates about it---------- or not as the case may be
Kind Regards, Andy
-
04-03-2006, 11:10 AM #9
Re: Blast freezer temperature problem. Please help!!!
Originally Posted by volta
and thus the oil pressure
Bulb temp is the desuperheating bulb for the interstage, the valve has been opened up too much
Kind Regards. Andy
-
04-03-2006, 11:17 AM #10
Re: Blast freezer temperature problem. Please help!!!
Hi
Discharge low
amps low
what about the head joint, two stage bitzers would blow the odd one.
Please fit new head joint and set desuperheat TEV
-
06-05-2010, 09:25 AM #11
Re: Blast freezer temperature problem. Please help!!!
am in africa and you can reach me on
griffine.ongaro@yahoo.com
ive installed more than five blast freezer around red sea and they are ok,just book aflight ill sort it out for you
thanks
-
06-05-2010, 11:15 PM #12
-
09-05-2010, 04:13 AM #13
-
10-05-2010, 04:54 AM #14
Re: Blast freezer temperature problem. Please help!!!
Hi there,
I assume your TEV is MOP type.
The head of TEV must be few degrees warmer than the bulb, if not the valve will close.
What I do in this applications is this : use wire type heaters, like the one used in drain pipes, connect this heater on top of the TEV and insulate it. the rest must be in the air, because every one meter of this heaters must be connected to electricity. Energize this heater when compressor is on.
The other issue you have to consider is the amount of sub-cooling. If you have sub-cooler, which you must, then you will get around 40°C sub-cooling. Select correct size of TEV orifice according to that sub-cooling. If not then your suction will be higher than it should be.
CheersEven Einstein Asked Questions
Similar Threads
-
Problem with freezer fan.
By fridg in forum FundamentalsReplies: 15Last Post: 13-04-2006, 01:51 AM -
Blast Freezer Questions
By rickmor in forum IndustrialReplies: 2Last Post: 11-04-2006, 08:15 PM -
Q=? h1=? mechanical schematics
By fridg in forum Technical SpeculationsReplies: 22Last Post: 19-03-2006, 02:43 PM -
Blast Freezer Evaporators Selection
By Mahmoud in forum FundamentalsReplies: 12Last Post: 21-09-2005, 04:31 PM -
Article in ACH&R News
By Gary in forum FundamentalsReplies: 8Last Post: 20-05-2003, 12:27 AM