Results 1 to 18 of 18
Thread: strange air conditioning device
10-07-2013, 09:33 PM #1
hi
i checked heatpump window type ac
its 2 ton
there is thin tube connecting beween the exit of the capillary tube and compressor bottom
what its utility
for oil return
or cooling compressor
or what
11-07-2013, 12:27 AM #2
Re: strange air conditioning device
I'd wager to cool the compressor giving where you are! oil will go with the refrigerent so normaly a dedicated return is not needed
Now in Redvers Sask.
I would agree with The MG Pony. Attached is a pic. It shows a reciprocating hermetic with the same oil cooling line.
11-07-2013, 10:37 AM #4
The oil cooling is not the same. The diag above will have an in/out circuit. His picture shows a simple refrigerant injection into the compressor body to aid cooling.
I realize were talking about 2 different compressors. That picture is to show him that some hermetic compressors have oil cooling. Are you suggesting that his compressor is muilti-stage?
11-07-2013, 01:09 PM #6
No not multistage, it is just a very cheap, yet reliable way to cool a rotary piston compressor, you rob 600btu/h from the cooling capacity and shunt it to the low side shell to cool the compressor.
11-07-2013, 04:00 PM #7
Mind you, I feel sorry for that compressor.
Have you noticed the marks half way up the casing where it has been beaten by a blunt object?Brian - Newton Abbot, Devon, UK
11-07-2013, 04:47 PM #8
11-07-2013, 05:43 PM #9
15-07-2013, 09:56 PM #10
ok
what happen if i removed the that line
somebody here said they removed it
and compressor get hot then overloaded
16-07-2013, 02:42 AM #11
Probable liquid injection discharge cooling for a scroll on a low temp application
17-07-2013, 01:50 PM #12
if you remove it, the compressor will cook and die in all probabilities
17-07-2013, 04:01 PM #13
now im confused
what is the utility
cooling or oil return or what
17-07-2013, 05:52 PM #14
17-07-2013, 06:46 PM #15
Wow RBartlett, interesting
18-07-2013, 12:30 AM #16
Its job is to cool the compressor by shunting a small amount of liquid to the suction/discharge of the compressor! with out this it will over heat and die due to the hi ambient temps!
08-09-2013, 09:34 PM #17
thank u all
please close thread
08-09-2013, 09:35 PM #18
thank u all