    Cooling Load for the SS tank



    We have a 650 Ltr Jackated tank (SS) for Purified Water Store with water temperature 80 C. We want to cool down the temperature up to 20 C withen 20 min for process requirement.
    Cooling media Chilled water with temperature 7 to 8 C. What will be the chiller Tonage Capacity? Pump flow rate will be matched with chiller, so does we need flow control valve for the tank or just circulation of coolin water is enough?
    Tank Dia: 2' and Max capacity of the tank 700 Ltr.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Cooling Load for the SS tank

    How much heat does your process add to the cooling water?

  3. #3
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Cooling Load for the SS tank

    135kw ..............

  4. #4
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    14

    Re: Cooling Load for the SS tank

    ............?

  5. #5
    Join Date
    Mar 2010
    Location
    Bangladesh
    Age
    40
    Posts
    151
    Rep Power
    14

    Re: Cooling Load for the SS tank

    650L ≈ 650kg.
    From steam tables,
    hf80degC - hf20degC = 251kj/kg.
    Total cooling needed = 251kJj/kg x 650kg = 163150kJ divided by 20min ≈ 160kW.

    Is it so................??

    Flow rate of pump or others data????

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Cooling Load for the SS tank

    650kg x 4.19 x 60 /1200 = 136.175kW

    136.175kW /(4.19x60) = 0.54 l/s flow rate

  7. #7
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Cooling Load for the SS tank

    650*4.18*60 = 163000/3600=45Kwhr
    60min/20mins = 3
    3*45 = 135kw
    "check"
    135Kj/s * (20 *60 =1200)=162000Kj, close enough after rounding

    That answers your question, but the question is wrong

    In reality for example your duty could 400Kw at the start and 20Kw at the end. unless you control flow to have a steady kw rating.