    Mar 2010
    Bangladesh
    34
    151
    9
    Cooling Load for the SS tank
    We have a 650 Ltr Jackated tank (SS) for Purified Water Store with water temperature 80 C. We want to cool down the temperature up to 20 C withen 20 min for process requirement.
    Cooling media Chilled water with temperature 7 to 8 C. What will be the chiller Tonage Capacity? Pump flow rate will be matched with chiller, so does we need flow control valve for the tank or just circulation of coolin water is enough?
    Tank Dia: 2' and Max capacity of the tank 700 Ltr.
    Oct 2001
    Nottingham UK
    5,127
    42
    Re: Cooling Load for the SS tank
    How much heat does your process add to the cooling water?
    I'm back on the Pale
    Aug 2009
    New Zealand
    54
    2,556
    135kw ..............
    Mar 2010
    Bangladesh
    34
    151
    9
    Mar 2010
    Bangladesh
    34
    151
    9
    650L ≈ 650kg.
    From steam tables,
    hf80degC - hf20degC = 251kj/kg.
    Total cooling needed = 251kJj/kg x 650kg = 163150kJ divided by 20min ≈ 160kW.
    Is it so................??
    Flow rate of pump or others data????
    Oct 2001
    Nottingham UK
    5,127
    42
    650kg x 4.19 x 60 /1200 = 136.175kW
    136.175kW /(4.19x60) = 0.54 l/s flow rate
    Aug 2009
    New Zealand
    54
    2,556
    650*4.18*60 = 163000/3600=45Kwhr
    60min/20mins = 3
    3*45 = 135kw
    "check"
    135Kj/s * (20 *60 =1200)=162000Kj, close enough after rounding
    That answers your question, but the question is wrong