    Heating / Cooling Control



    There is a demand for close temperature control systems with heating and cooling regulation. Heating is easy! A thyristor current controller and a self-tuning, PID temperature controller will give ± 1°C of the setpoint. Cooling is a problem! With a conventional liquid line solenoid valve, the time taken for the compressor to start and get any cooling effect in the evaporator means that the room temperature is racing upwards. What is needed is to keep the compressor running continuously so that cooling is available immediately it is requested. Refrigeration engineers mumble the words “hot gas by-pass”. If you have any other ideas …



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Heating / Cooling Control

    For close control applications I find it better to use chilled water

  3. #3
    Join Date
    Jan 2006
    Location
    UK
    Posts
    53
    Rep Power
    19

    Re: Heating / Cooling Control

    Frank, I agree, CW is a very good medium to use for close temperature control. However, it is only available with big companies. The usual scenario is a relatively small company with a single close temperature chamber, no CW on site. In these circumstances, a DX evaporator appears to be the only answer. Hence the question. Being only an electrical engineer, I am hoping for some ideas from you refrigeration wizards out there!

  4. #4
    Join Date
    Aug 2001
    Location
    Christchurch, Dorset UK
    Posts
    3
    Rep Power
    0

    Re: Heating / Cooling Control

    I've used pulsing Hot-Gas for close cooling control to +/- 0.2K on chilled water systems, but only when there is no heating. The problem with heat+cool PID control is that they fight. Its better to over cool and control the temp accurately by heating and have enough heating to substitute the load to keep the (on/off) compressor running. This way, using a Thyristor, you can get very accurate control. It is also better to use chilled water which is easier to manipulate than a DX gas. In any event, once the compreeor stops, you can say good by to close control.

    Good luck & up the cherries.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Heating / Cooling Control

    In the projects I have worked on where similar requirements are needed for continuous operation hot gas bypass is the only way to go for small to medium applications.

    Using hot gas bypass to false load the evaporator and compressor provides continuous operation for close humidity and cooling control. The hot gas is controlled by an outlet pressure regulator which senses the evaporator pressure.

    When the evaporator pressure decreases due to a reduction in heat load to the coil, the bypass regulator modulates open to control the evaporator pressure.

    The hot gas is usually introduced downstream of the TXV, but before the refrigerant distributor to provide good mixing of the hot gas and liquid (from the TXV).

    Hot gas can also be introduced into the suction line upstream of the compressor, but in this case you will also need some liquid refrigerant injection to desuperheat the suction gas before it enters the compressor.

    Without the liquid injection, the compressor can overheat due to the high inlet gas temperature.

    I also agree with Franks' statement that chilled water works quite well. The mass of cold water being circulated provides a dampening effect for temperature rise.

    Depending on the type of load, you might also want to consider a water storage tank to provide sufficient reserve cooling capacity to allow the refrigeration system (chiller) to control the temperature and cooling load.
    Last edited by US Iceman; 24-02-2006 at 03:11 PM. Reason: spelling

  6. #6
    rbartlett's Avatar
    rbartlett Guest

    Re: Heating / Cooling Control

    what about inverter ?

    cheers

    richard

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Heating / Cooling Control

    Quote Originally Posted by rbartlett
    what about inverter ?
    This another method, but you have to ensure the evaporator liquid feed control is capable of operating at reduced capacity.

    At some point if the load reduces sufficiently the inverter will try to slow the compressor down too slow and you can loose oil pressure. So you have some minimum capacity still available.

    If the system cooling load is lower than the minimum capacity reduction of the system you can still have problems with short-cycling or loss of temperature control.

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Heating / Cooling Control

    The usual scenario is a relatively small company with a single close temperature chamber, no CW on site.
    Have a look here. There are also other sites that have chillers down to 5kw. http://www.daikin.co.uk/aircondition...s/euwa-kzw.jsp

  9. #9
    Join Date
    Dec 2005
    Location
    South East England
    Age
    56
    Posts
    155
    Rep Power
    19

    Re: Heating / Cooling Control

    When I was working on rooms for the storage of pharmaceuticals it called for a stability of +/- 0.1 deg. C. They had refrigeration running 24/7 & heating rated at 50% more powerful than the refrigeration. The heat would be pulsed to maintain the temp. with a self-tune controller (very wasteful from an energy consumption point of view) & the humidity was controlled +/- 5% RH with a small water boiler controlled by a 2nd channel on the controller.
    Noah had to leave the dinosaurs behind as they would've sunk the boat.

  10. #10
    pradyutghose's Avatar
    pradyutghose Guest

    Re: Heating / Cooling Control

    From where I can get the RLA of Kirloskar Copeland sealed compressor?

  11. #11
    pradyutghose's Avatar
    pradyutghose Guest

    Re: Heating / Cooling Control

    Sir,
    I am not getting proper cooling, if anybody can suggest.
    Compressor:1.5 TR
    Evaporator : 375 x 375 mm x 4 row
    Suction Pressure : 70 psi
    Discharge : 290 psi
    Ambient : 34 DegC
    Air Flow : 350 cfm
    Compressor: Copeland make/Hermatic-Sealed
    I am not getting coil temperature less than 10 Deg C Why?

  12. #12
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Heating / Cooling Control

    Quote Originally Posted by pradyutghose
    Sir,
    I am not getting proper cooling, if anybody can suggest.
    Compressor:1.5 TR
    Evaporator : 375 x 375 mm x 4 row
    Suction Pressure : 70 psi
    Discharge : 290 psi
    Ambient : 34 DegC
    Air Flow : 350 cfm
    Compressor: Copeland make/Hermatic-Sealed
    I am not getting coil temperature less than 10 Deg C Why?
    Without air on to the coil conditions its impossible to say, however it seems the cooling is uncapacity, or the compressor is struggling. If the gas is R22 and the head is 290 psig with a ambient of 34deg c it would indicate an under sized cooling system.

    Kind Regards, Andy

Similar Threads

  1. underfloor heating and cooling
    By Lc_shi in forum New Technologies
    Replies: 19
    Last Post: 11-12-2009, 12:22 PM
  2. Replies: 21
    Last Post: 05-07-2008, 10:48 AM
  3. radiant cooling and heating issue
    By Lc_shi in forum Fundamentals
    Replies: 2
    Last Post: 29-05-2006, 08:34 AM
  4. air cooling and heating coil test
    By Lc_shi in forum Technical Speculations
    Replies: 8
    Last Post: 23-02-2006, 01:15 AM
  5. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 01:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •