Results 1 to 5 of 5
  1. #1
    Join Date
    Aug 2013
    Location
    Denmark
    Age
    31
    Posts
    27
    Rep Power
    0

    Capillary tube and TEV



    Which is the most reliable when thinking about great temp/pressure difference between high side and low side for eksample evap: 15 degc condens: 55degc?



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Capillary tube and TEV

    .

    Its not that simple

    Capillary tubes are basic, they have no moving parts and
    are very cheap. Cap tubes have their place but there is
    no control over a cap tube. it gives a prescribed pressure
    drop over its length. If you require more then you need
    something that can be controlled or adjusted and that is
    where the Thermostatic Expansion Valves (TEV), Electronic
    Expansion Valves (EEV) came into play.

    TEV's are fairly bullet proof and do their job well but because
    of a mechanical delay inside the valve they need a wide-ish
    superheat to be able to control safely so that means a %
    of the evaporator is not used for heat exchange (it is only used
    to superheat the refrigerant vapour).

    EEV's have much more control so they can have less fluctuations
    regarding the amount of liquid in the evaporator at any time.

    Horses for courses is what we say

    The application dictates the choice and there are hundreds
    of considerations to take into account.

    The biggest consideration is cost.........

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Aug 2013
    Location
    Denmark
    Age
    31
    Posts
    27
    Rep Power
    0

    Re: Capillary tube and TEV

    Thank you for your reply

  4. #4
    Join Date
    Aug 2013
    Location
    Denmark
    Age
    31
    Posts
    27
    Rep Power
    0

    Re: Capillary tube and TEV

    I was wondering, if the capillary tube gives a prescribed pressure drop, what would happen if the ambient or the room temperature changes. And what if ambient temperature stays constand and only room temperature changes. If for eksample the ambient is 55c and room is 30c, and the room temperature falls to 25c but ambient stays 55c.

  5. #5
    Join Date
    Aug 2013
    Location
    DK
    Age
    32
    Posts
    27
    Rep Power
    0

    Re: Capillary tube and TEV

    I have a question too about this subject, what if you have an ambient of 55 celsius, a condensing temp of 60 cesius and a evaporator temp on 20 celsius, what will happen if a capillary tube is used and the ambient drops to ex. 20 celcius, what will happen?
    I'm wondering about how this will affect the system and if the condensing and evaporating temperatures will change?

    Regards

    Michell