    Daikin RZQ125D7V1B



    Hi all hope everyone is well

    Had a call out to a Daikin split serving a server room. Customer said unit is not cooling. On arrival sure enough server room very warm but not as hot as you would think without any cooling. Checked indoor coil cold at inlet but soon losing cooling about a quarter of the way round (cassette). faulty metering device, restriction, partially blocked filter drier, lack of refrigerant. At the outdoor unit the liquid line was sweating away, suction pipe nothing. Put gauges on 10 bar suction 11 bar liquid ?????? We are on R410A by the way. Discharge nice and hot into reversing valve (Heat pump on server room application) and then into condenser coil. Condenser coil not even warm almost feels cool off fans. Maybe not quite as straight forward as I thought. Liquid line not warm to the touch all the way to what I assume is a electronic expansion valve. Pipe sweating leaving the EEV. Decided to switch unit off and restart. On start up the suction pressure dropped to 4 bar before steadily creeping back unto 10 bar which is where I was before. Could it be a restriction in the condenser coil ?. At the minute I definitely think we have a restriction somewhere however the 10 bar suction pressure is puzzling me. Think I'm gonna put some temp cooling in and sleep on it. Any advise welcome and if anyone has a link to the service manual that would be great. Sometimes when your this tired you just tie yourself in knots. Cheers guys



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin RZQ125D7V1B

    Sounds over charged

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin RZQ125D7V1B

    run it in test heating see if pressure on suction pipe goes to 33 bar
    go setting mode 41 read the air,coil sensor-hold test for 8 seconds- shows setting mode 10 then release and hold for a further 8 seconds then temp up (changes 40 alarm history to 41 sensor values)
    any fault codes?

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Daikin RZQ125D7V1B

    OK,
    Before you go too far down the troubleshooting route, what is the humidity like in the room?
    If it is below 35% then your unit is likely to go in to "frost prevention" mode and therein lies your problem...


  5. #5
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    178
    Rep Power
    15

    Re: Daikin RZQ125D7V1B

    The system has been in use since 2010 without problem. No work other than routine maintenance carried out. Charge is recorded as factory pre charge although the pipe run is prob only 5m. I will take a closer look tomorrow and check for fault codes. I will take a reading of the rooms humidity however it did feel over 35% but will check. Something which I failed to mention before was that the amber led H3P HWL was illuminated showing a fault approximately 10 mins after start up.

  6. #6
    Join Date
    Aug 2009
    Location
    Manchester
    Posts
    178
    Rep Power
    15

    Re: Daikin RZQ125D7V1B

    I did check 40 alarm history when I arrived nothing shown. But will interrogate the controller further tomorrow now I have a bit more know how. Thanks

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin RZQ125D7V1B

    http://www.mediafire.com/download/p8...bv5n/rzq_d.pdf
    big manual- happy reading- hope its not one of my installs!!!

  8. #8
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Daikin RZQ125D7V1B

    Quote Originally Posted by Kirky View Post
    The system has been in use since 2010 without problem.
    OH, good.
    Then there is no chance that their IT guys would have added more load.

    Once I were called in to a site where another engineer had spent 2 days investigating why the CRAC units no longer performed. Over the years there had always been 3 units running and one unit in stand by but now not even with all 4 units operating could the room temp be maintained.
    The facilities manager and the IT guys insisted that they hadn't added any new kit...
    Well, come 5pm when the nightshift's IT manager came on duty the problem was solved in 5min flat.
    The weekend before (this must have been on a Wednesday) they had upgraded all their servers to the latest generation blade servers. (=16 kW load per rack instead of the 4 kW of the old servers)



  9. #9
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Daikin RZQ125D7V1B

    Quote Originally Posted by install monkey View Post
    http://www.mediafire.com/download/p8...bv5n/rzq_d.pdf
    big manual- happy reading- hope its not one of my installs!!!
    he did say it was still running

  10. #10
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: Daikin RZQ125D7V1B

    Quote Originally Posted by frank View Post
    Sounds over charged
    Ditto this

  11. #11
    Join Date
    Nov 2007
    Location
    athens
    Age
    52
    Posts
    28
    Rep Power
    0

    Re: Daikin RZQ125D7V1B

    i would remove and recharge with fresh refrigerant...

  12. #12
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Daikin RZQ125D7V1B

    Have you tried a pump down, this sounds like it could well be an inefficient compressor.

    I had the same fault a few weeks ago.

    The compressor was ramping up to about 70hz but suction pressure was still around 10-11bar on R410a, with an air onto the Evap of 26degC
    The difference between genius and stupidity is that genius has its limits.