Results 1 to 5 of 5
Thread: Optimum condenser fan speed
-
24-02-2006, 04:04 AM #1
Optimum condenser fan speed
If a condenser is speeded up, airflow will increase and the condenser temperature will decrease, making the system more efficient (ignoring the power used by the condenser fan). But at some point, the energy used by the fan motor will undo the savings from lowered condenser temperature.
Is there a "fast and simple" way to calculate the optimum fan speed or does it vary too much depending on the design? (This is all just for curiousity, BTW.)
-
24-02-2006, 03:29 PM #2
Re: Optimum condenser fan speed
Originally Posted by star882
I have seen this happen on large ammonia systems also. In the attempt to reduce the discharge pressure to some lower pressure you can expend considerable fan energy to save energy on the compressor motors.
You need to develop some sort of a model that accounts for fan energy and compressor motor energy compared to ambient conditions and condenser capacity to see the results.
Depending on the size of the system and the costs you are able to spend, you can use a VFD to incrementally decrease the fan speed. This will provide energy savings on the fan power, close discharge pressure control, and allow you to minimize the problem you have stated.
-
25-02-2006, 08:42 AM #3
Re: Optimum condenser fan speed
You can simulate this in Microsoft Excel with the function "iteration"
I'm plotting it out in a graph, is much easier for me.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
27-02-2006, 01:31 AM #4
Re: Optimum condenser fan speed
You can simulate this in Microsoft Excel with the function "iteration"
There is one thing I want to add, increasing air volume will enhance the condenser heat rejection,but it's without obvious effect while reaching one point. Only lifting air side heat transfer coefficient can't increase total K value. So the optimum value should think both the power consuming and K value improvement.
rgds
LCI hear...I forget;I see...I remember;I do...I understand
-
27-02-2006, 01:50 AM #5
Re: Optimum condenser fan speed
Originally Posted by lc_shi
Similar Threads
-
Condensor split temperature
By Peter_1 in forum FundamentalsReplies: 14Last Post: 31-07-2011, 05:49 PM -
method to design air cooled condenser
By abbasi in forum New TechnologiesReplies: 4Last Post: 12-02-2008, 08:34 AM -
Cooling condenser of split with condensate from evaporator
By smileypete in forum Air ConditioningReplies: 11Last Post: 10-07-2005, 08:21 AM -
Condenser Fan
By Vicky in forum Supermarket RefrigerationReplies: 3Last Post: 20-04-2005, 08:38 AM -
Kuba fan speed question
By Peter_1 in forum ElectricalReplies: 1Last Post: 07-12-2004, 07:17 PM