    Condenser temperature according to the ambient



    Hey

    I am working on a project in which we have an ambient temperature on 55 degree celsius, and most of the compressors that are out there will only be able to deliver a condensing temperature of 60 degree celcius, will this be enough for the heat to flow from the condenser to the ambient air?

    Normally i would of course go for 10-15 degree celcius higher than the ambient, but since this application probably will be used in desert/jungle environment such high ambient temperatures is to be expected !


    Regards
    Michell



  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser temperature according to the ambient

    You will find that the power used, may very well affect the allowable Tc,sat (condensing temp) allowed for the compressor.

    We've seen the US version rated closer to 62.5'C (at 110V), while the European/UK/South Africa/Australia version could run up to 70-75'C. (Refer back to a thread by Gary & myself, some years ago, where we discussed this).

    Heat-pump compressors can run hotter than standard refrigeration systems. In the end though, your overall COP will be poor.

    You may have to pull a few more technical tricks to achieve your end goal.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Condenser temperature according to the ambient

    Quote Originally Posted by WootAC?? View Post
    most of the compressors that are out there will only be able to deliver a condensing temperature of 60 degree Celsius
    Appels and pears...

    The compressor doesn't know what the actual condensing temperature is, and it doesn't even care as long as it itself is cool enough.
    The data you will have to look for is the maximum operating discharge pressure and then select the refrigerant accordingly. When you look at the data sheets for the compressors they will only tell you the "optimum design envelope" as when you go outside this the performance drop quite significantly but this is not to say that the compressor won't operate outside these conditions.

    You might have to add liquid injection to the suction line to keep the compressor and the oil cool enough but as long as you keep below maximum discharge pressure the compressor should keep on pumping.


  4. #4
    Join Date
    Aug 2013
    Location
    DK
    Age
    32
    Posts
    27
    Rep Power
    0

    Re: Condenser temperature according to the ambient

    I was actually just hoping for an yes or no answer, but I will look into the informations given :-)


    Regards
    Michell

  5. #5
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condenser temperature according to the ambient

    Precious few yes/no answers in the RHVAC game. A world of balanced options.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  6. #6
    Join Date
    Mar 2008
    Location
    Melbourne, Australia
    Age
    40
    Posts
    48
    Rep Power
    0

    Re: Condenser temperature according to the ambient

    Yes it can be done, R134a would probably be the optimum refrigerant and the condeser sized on a low TD.

  7. #7
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Condenser temperature according to the ambient

    Copeland Scroll max SCT 75C and 0C SST on R134a. No issue with your 55C ambient

  8. #8
    Join Date
    Aug 2013
    Location
    DK
    Age
    32
    Posts
    27
    Rep Power
    0

    Re: Condenser temperature according to the ambient

    Thanks for the answers :-)


    Regards
    Michell