    30 XA low oil pressure reading



    Problem:
    On temperature achievment the unit shuts down, the oil differential pressure reads
    b to -1.04 and this condition appears on both the chillers for circuit A only.
    Action:Removed the transducers and inter-changed from other circuit known to be O.Kresults are same. Checked all hard wiring, cables and receptacles and terminating jacks, all O.K.Installed gauge with the transducers in question, to monitor actual pressure during fault conditions, gauge pressure is at positive, readings for the Diff. Oil Pressure at shut down on the display parameters goes to 0.04 to -1.04, at 0.04 it is still normal as the readings come down to -0.04 to -1.04 an alarm is generated and will have to be reset before the demand is called for cooling.



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: 30 XA low oil pressure reading

    Change the oil filters