Results 1 to 3 of 3
-
29-07-2013, 11:07 PM #1
Next control and monitoring systems
Hi Guys anyone worked on the Next control and monitoring system, I guess its a similar system to the RDM, I have not been given any info or log in details yet so making it difficult to work on, I have two serve overs controlling lower than they are set to (although I cant get in to parameters to check) and one unit flashing pd of witch I'm assuming this is a probe fault. I have been told there will be a hand held reader sent to site for next visit to use, but could do with a little info before I get there
-
31-07-2013, 11:50 AM #2
Re: Next control and monitoring systems
Hi Seacold,
PM me your e-mail address and i'll send you what I have
Regards,
Mel.Mostly found nowadays at the sharp end of the stick!
-
27-08-2013, 08:01 PM #3
Re: Next control and monitoring systems
PD might be pull down, the RDM units control to below setpoint by the differential, setpoint is cut in rather than cotout, but this is RDM.
alecMostly found in the southern part of this green and pleasant land.