    Sizing suction and discharge headers



    Hi Guys

    Im trying to make a design for two compressors built in parallel... now the problem is that i must connect the suction and discharge to headers and i can not find the way of calculating the size of the header...

    I hope any of you can give any procedure or lead me to any reference, Ashrae or trane or any other reference...I have all of them but they only state the way of sizing a single discharge or suction line,

    much appreciated

    Thanks in advance



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    22

    Re: Sizing suction and discharge headers

    go to this link,it may help you....

    http://www.bitzer.de/eng/productservice/p4d/KT-600

  3. #3
    Join Date
    Dec 2012
    Location
    Lebanon
    Posts
    14
    Rep Power
    0

    Re: Sizing suction and discharge headers

    hey moideen,
    Thanks but i already have this catalogue from bitzer, but it never states any rules or calculations for it.
    I need some rules, lets say i have the 3 compressors ( same type and capacity ) in parallel and i want to connect the suction lines ( must ) to a header as well as the discharge lines...
    How to choose the correct size of headers ?

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Sizing suction and discharge headers

    Quote Originally Posted by salahzantout View Post
    hey moideen,
    Thanks but i already have this catalogue from bitzer, but it never states any rules or calculations for it.
    Yes, it states! Suction header=<4m/s rule, discharge header=sum of individual pipes rule. Read carefuly!
    Last edited by nike123; 26-08-2013 at 07:15 AM.

  5. #5
    Join Date
    Dec 2012
    Location
    Lebanon
    Posts
    14
    Rep Power
    0

    Re: Sizing suction and discharge headers

    Quote Originally Posted by nike123 View Post
    Yes, it states! Suction header=<4m/s rule, discharge header=sum of individual pipes rule. Read carefuly!
    hey nike,

    yea ive seen this... and actually i already know this... its in 2.6 and 2.9 i think
    but i want little more details...

    lets say i have two suction lines of identical compressors in parallel
    1 inch suction line with capacity of 15 kw each

    do i select the header as 30 kw with velocity restrictions ??

  6. #6
    Join Date
    Dec 2012
    Location
    Lebanon
    Posts
    14
    Rep Power
    0

    Re: Sizing suction and discharge headers

    also note that im working with screw compressors....

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Sizing suction and discharge headers

    You should size suction header in such way that maximum velocity of gas does not go above 4m/s.
    You need to select moment in operation of such tandem in which you have maximum mass flow of refrigerant and size header pipe to have velocity in that moment less than 4m/s.

    In your example, yes you size it at 30kW if that is maximum sum of individual capacities.

  8. #8
    Join Date
    Dec 2012
    Location
    Lebanon
    Posts
    14
    Rep Power
    0

    Re: Sizing suction and discharge headers

    what about minimal capacity ??

    is there any manual you have for exact calculations ?

  9. #9
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Sizing suction and discharge headers

    Hi, salahzantout

    Quote Originally Posted by salahzantout View Post
    what about minimal capacity ??

    is there any manual you have for exact calculations ?
    It is easy...when you make drawings of your plant you can upload them here and we'll tell you what you can do in some better way, if ... it is a game, unfortunately the best is not always acceptable by client due to high price


    You can try this software ...

    ftp://software.danfoss.com/RA/DirCalc/DirCalc.zip

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Sizing suction and discharge headers

    I am not construction engineer. I cannot tell you with 100% certainty what you should do in that case. I just interpreting what is said in that paper from Bitzer and what I saw in practice on few installations, that work satisfactory.
    In today discussion with my colleagues, minimal capacity is not of concern in designing that, only maximal! And that correspond with what is written in that Bitzer manual.

    Also, as in that manual, discharge header should be dimensioned as sum of cross section of all individual discharge pipes and not less than that.
    Discharge pipe on individual compressor should not be smaller than factory prepared (proscribed) connection at compressor discharge isolation valve for single use.

  11. #11
    Join Date
    Dec 2012
    Location
    Lebanon
    Posts
    14
    Rep Power
    0

    Re: Sizing suction and discharge headers

    hey nike

    actually mimimal capacity is important so that you insure sizing the pipes for getting oil back to the compressor

    Also note that bitzer recommendation is for reciprocating compressors and not screw...

    but thanks anyway

  12. #12
    Join Date
    Dec 2012
    Location
    Lebanon
    Posts
    14
    Rep Power
    0

    Re: Sizing suction and discharge headers

    Quote Originally Posted by Josip View Post
    Hi, salahzantout



    It is easy...when you make drawings of your plant you can upload them here and we'll tell you what you can do in some better way, if ... it is a game, unfortunately the best is not always acceptable by client due to high price


    You can try this software ...

    ftp://software.danfoss.com/RA/DirCalc/DirCalc.zip

    Best regards, Josip
    Hey Josip...
    thanks for that... i ll try to learn on using it... but i wish you just link me to some manuals or ebooks for calculating the pipe sizes... i am not asking for sizing a single compressor one capacity system... i am asking for multiple compressor system which requires headers and so on

    ive seen ashrae, carrier, trane, mc quay and some more but nothing states some real calculations with examples for multiple compressors or evaporators... etc etc

    so if you would link me to any valuable book or even you own calculations ( if it is possible ) I woulld be so thankful

  13. #13
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Sizing suction and discharge headers

    Hi, salahzantout


    Quote Originally Posted by salahzantout View Post
    Hey Josip...
    thanks for that... i ll try to learn on using it... but i wish you just link me to some manuals or ebooks for calculating the pipe sizes... i am not asking for sizing a single compressor one capacity system... i am asking for multiple compressor system which requires headers and so on

    ive seen ashrae, carrier, trane, mc quay and some more but nothing states some real calculations with examples for multiple compressors or evaporators... etc etc

    so if you would link me to any valuable book or even you own calculations ( if it is possible ) I woulld be so thankful
    I'm glad you found Danfoss software useful ...

    this one CoolPack 1.5 is very good too ... very complex too ....
    http://en.ipu.dk/~/media/koele-og-en...olpack150.ashx

    maybe you can find something here too ..
    http://softadvice.informer.com/Refri...g_Program.html

    With books you can start here ...

    http://www.gobookee.net/refrigerant-...ng-calculator/

    then visit this very valuable link ....

    ...http://www.refrigeration-engineer.co...geration-Books

    here you will find links to books ... need some time to read all threads and much more time to read books but that time is not a lost time at all ...


    Sorry, my calculations are not of any value for you ... my systems are completely different of yours and it is not written like a school book with explanation why this and why that ... more like small notes .... and it is useless for any other person too ... I'm using above software too

    It is not hard to calculate, pipe or header sizes ... more important and harder is to make complete piping layout, with slopes, vertical distances for risers, bottom, side or top pipes joint, supports ... etc ... this is something what is not possible to learn from books or some software ... to design refrigeration plant it is a must to have a lot of experience ....

    again, my suggestion, the best is to make your "homework" and then we can advice you, but this is only my opinion and I can be wrong, anyhow, it is your decision what you'll do ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  14. #14
    Join Date
    Dec 2012
    Location
    Lebanon
    Posts
    14
    Rep Power
    0

    Re: Sizing suction and discharge headers

    ok will check the links

    thanks alot Josip
    much appreciated