    re-commisioning R404a cold room...



    Hi all been doing Air con for a few years but company i was with went down the pan.. 8(

    have started with a new firm and have got to re commision a r404a cold room

    just wanted to ask a few pointers as never even used 404a..

    the room needs to be -18c and im hoping a sight glass is fitted..

    after a good vac etc should i be able to just charge to a full sight glass to get room to -18c or is it gonna be a case of taking temps onto evap and compare to suction pressure/temp??

    any help will be great help!!!



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: re-commisioning R404a cold room...

    A sight glass will be useful but don't expect it to indicate what you want until the room is down to temperature.

    Be aware that the compressor may be overloaded on pull down, depending on equipment fitted of course, so be prepared to throttle it back until the load eases.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: re-commisioning R404a cold room...

    and remember that R-404 should be filled only as liquid!!

  4. #4
    Join Date
    Aug 2013
    Location
    england
    Posts
    3
    Rep Power
    0

    Re: re-commisioning R404a cold room...

    thnx guys...

    so at start off room will be 20c ish what sort of suction/high side would you think to see?

    and at -18c 1bar ish??

    thnx

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: re-commisioning R404a cold room...

    At -18 it should be 25 psi, thats -23 evaporating temp.
    Check and correct the superheat at about -15,[only if you need to]

  6. #6
    Join Date
    Aug 2013
    Location
    england
    Posts
    3
    Rep Power
    0

    Re: re-commisioning R404a cold room...

    Quote Originally Posted by chemi-cool View Post
    At -18 it should be 25 psi, thats -23 evaporating temp.
    Check and correct the superheat at about -15,[only if you need to]
    Nice one..

    after a change of drier and a good vac ill bomb charge with liquid and hopefully see that temp drop!!!

  7. #7
    Join Date
    Jan 2007
    Location
    South East
    Age
    48
    Posts
    10
    Rep Power
    0

    Re: re-commisioning R404a cold room...

    My advice would be to get an in date comparator, they even do an app for that these days