    Lightbulb will liquid receiver make flash gas?



    Dear friends,
    I have some questions about liquid receivers.
    1. Why not using liquid receivers in air-condition systems? i have seen the usage of receivers in mostly in low temperature applications.
    2. As refrigerant enter to the liquid receiver, it expands and create flash gas. Will it reduce the system capacity? Or will this flash gas again condensed to liquid?
    May be my questions are blunder, but please I need some clarifications……



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: will liquid receiver make flash gas?

    .

    The discussion on what happens inside a receiver is one that crops up quite often and
    it does create huge debate.

    Receivers are used when you have a Thermostatically Controlled Expansion valve (TEV)
    or a Electronic Expansion Valve (EEV). Because the valve opens and closes, it requires a reserve
    of liquid to feed it so that is where the receiver comes in.

    In AC systems they sometimes use an over sized condenser and the liquid is stored in
    the bottom of the condenser.

    Some AC systems only use a capillary tube and they do not need a receiver at all.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    20

    Re: will liquid receiver make flash gas?

    Quote Originally Posted by Rob White View Post
    .

    The discussion on what happens inside a receiver is one that crops up quite often and
    it does create huge debate.

    Receivers are used when you have a Thermostatically Controlled Expansion valve (TEV)
    or a Electronic Expansion Valve (EEV). Because the valve opens and closes, it requires a reserve
    of liquid to feed it so that is where the receiver comes in.

    In AC systems they sometimes use an over sized condenser and the liquid is stored in
    the bottom of the condenser.

    Some AC systems only use a capillary tube and they do not need a receiver at all.

    Regards

    Rob

    .
    I couldn't have said it better!

  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: will liquid receiver make flash gas?

    1) ac systems usually are dx evaporators & condensers ( water cooled ) act like a condenser cum receiver ..... Air-cooled condensers usually are installed with receivers to avoid reduction in condenser capacity due to liquid

    2) the flash gas in receiver will not liquify as long as the plant operates. After te plant shuts down gas could condence if surrounding temp drops

    d d koranne