    dry air for pressure test



    is there any harms to refrigeration system to use dry air for pressure test instead of Nitrogen gas? I've doubt on it but I've got no related info. Welcome your input


    best regards
    LC


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    Jun 2005
    Location
    California
    Posts
    395
    Rep Power
    19

    Re: dry air for pressure test

    Quote Originally Posted by lc_shi
    is there any harms to refrigeration system to use dry air for pressure test instead of Nitrogen gas? I've doubt on it but I've got no related info. Welcome your input


    best regards
    LC
    Found this in "The news" :Combining an oxidizing gas, such as oxygen or air, with an HCFC or HFC refrigerant under pressure can result in a fire or explosion.

  3. #3
    Join Date
    Feb 2006
    Location
    Poland
    Posts
    5
    Rep Power
    0

    Re: dry air for pressure test

    Refrigeration oil + high pressure oxygen = explosion

    Regards

Similar Threads

  1. Daikin VRV II Test Mode Failure
    By KISS KISS BANG in forum Air Conditioning
    Replies: 8
    Last Post: 30-05-2010, 08:54 PM
  2. air cooling and heating coil test
    By Lc_shi in forum Technical Speculations
    Replies: 8
    Last Post: 23-02-2006, 02:15 AM
  3. Annual Leak Test
    By Dave Finlay in forum Air Conditioning
    Replies: 9
    Last Post: 04-04-2004, 12:35 PM
  4. `skills / trade test???????
    By pagey in forum Chit Chat & Service Stories
    Replies: 26
    Last Post: 24-03-2004, 04:31 PM
  5. Evaporator Fan Test and Selection
    By pcle in forum Trouble Shooting
    Replies: 0
    Last Post: 18-11-2003, 04:10 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •