    Aug 2013
    DK
    27
    27
    cross-charge expansion valve
    Hello
    i have stumbled upen the term cross-charge expansion valve, could someone explain this to me?
    regards
    May 2012
    54
    1,330
    30
    Re: cross-charge expansion valve
    In the bulb there is a refrigerant that is used to open and close the valves diaphragm
    dependent on the amount of pressure inside it at the time.
    The refrigerant in the bulb tends to be the same as the refrigerant inside the system.
    If for reasons of control they put a different refrigerant in the bulb to that used inside
    the system, they call this a cross charge.........
    Refrigerants react to certain temps and pressures so if we want something to react
    differently we put a different refrigerant in........ Cross charged.
    Rob
    Aug 2013
    DK
    27
    27
    Well that is actual quite simple then, thanks for the fast answer !
    May 2012
    54
    1,330
    30
    Quote Originally Posted by WootAC?? View Post
    Fridge guys are quite simple........
    Rob
    May 2006
    India
    68
    400
    13
    Go through sporlan selection catalogue or book by roy j dosat..........principles of rerigeration
    d d koranne