    John0246



    Hey guys, had a look at a walk in freezer. The system is on R404a. Evaporator iced up due to defective thermostat, the liquid line drier was also blocked as I had a low suction pressure. Replaced the drier and thermostat, defrosted the evaporator but its still icing up. Checked the heaters and they draw 3.2 amps each, any ideas what would cause this.



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: John0246

    the drain is clear i presume,this could cause the fans to whip the water straight back on the evap if it does not get away

  3. #3
    Join Date
    Apr 2008
    Location
    Canada
    Posts
    253
    Blog Entries
    4
    Rep Power
    21

    Re: John0246

    Is the whole coil icing up? If so:

    Is the defrost clock setup correctly? Is the defrost period long enough? Do you have enough defrosts per day? Does the defrost terminate on time or temperature? If temperature, perhaps that termination control needs to be tested.

    Do you have proper airflow across the evaporator?

    If the coil is only partially icing up and it is occurring from the outlet of the txv throughout the first half of the evaporator, you are then low on gas.

  4. #4
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: John0246

    Hi John
    Have you checked the TXV bulb location?
    Have you checked the TXV superheat?
    Have checked the charge?
    have you checked the condenser is clean?
    What are the operating conditions?
    There are many reasons that an evap will ice up, some more info would be good.
    Paul

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: John0246

    Quote Originally Posted by john0246 View Post
    Hey guys, had a look at a walk in freezer. The system is on R404a. Evaporator iced up due to defective thermostat, the liquid line drier was also blocked as I had a low suction pressure. Replaced the drier and thermostat, defrosted the evaporator but its still icing up. Checked the heaters and they draw 3.2 amps each, any ideas what would cause this.
    Your suction pressure will always be low when the evap is iced up/airflow blocked, as there is insufficient heat to absorb.
    Similar symptoms on air conditioning units when the indoor coil is iced, dirty or filters blocked, leading to an incorrect diagnosis of SOG.