    how to calculate actual air cooled condenser TD.



    Hi,
    I have a doubt, as we know the TD of air cooled condenser is the difference between the saturated condensing temperatures minus air entering temperature. But my question is what we consider the as saturated pressure is compressor discharge pressure or liquid line pressure. My chiller display is showing the saturated pressure is the compressor discharge head pressure.



  2. #2
    Join Date
    Apr 2008
    Location
    USA
    Age
    45
    Posts
    7
    Rep Power
    0
    It's the head pressure and an air cooled condenser TD is the difference in between the entering and leaving temperature of the air through the condenser.

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: how to calculate actual air cooled condenser TD.

    Quote Originally Posted by saintmichael36 View Post
    condenser TD is the difference in between the entering and leaving temperature of the air through the condenser.
    No that's Delta T (ΔT)
    TD is is condensing temperature - air in
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: how to calculate actual air cooled condenser TD.

    Quote Originally Posted by beeran View Post
    Hi,
    I have a doubt, as we know the TD of air cooled condenser is the difference between the saturated condensing temperatures minus air entering temperature. But my question is what we consider the as saturated pressure is compressor discharge pressure or liquid line pressure. My chiller display is showing the saturated pressure is the compressor discharge head pressure.
    How far is your condenser away from your compressor?

    Your gauge is NOT reading the compressor discharge pressure,
    it is reading the condenser saturation pressure, the pressure
    you read at the compressor will be the pressure inside the condenser,
    unless it is many meters away, at another part of the build.

    So you can use the compressor discharge pressure for the saturation
    temperature of the condenser.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  5. #5
    Join Date
    Jan 2009
    Location
    dubai
    Age
    42
    Posts
    11
    Rep Power
    0

    Re: how to calculate actual air cooled condenser TD.

    Quote Originally Posted by Rob White View Post
    How far is your condenser away from your compressor?

    Your gauge is NOT reading the compressor discharge pressure,
    it is reading the condenser saturation pressure, the pressure
    you read at the compressor will be the pressure inside the condenser,
    unless it is many meters away, at another part of the build.

    So you can use the compressor discharge pressure for the saturation
    temperature of the condenser.

    Rob

    .
    Thanks your replay, this is single package air cooled chiller, carrier 30gh.discharhe and liquid line pressure difference is 30 psig. My question is to calculate the condenser TD, subtract the air temperature from discharge head pressure or liquid line pressure?

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: how to calculate actual air cooled condenser TD.

    Quote Originally Posted by beeran View Post
    Thanks your replay, this is single package air cooled chiller, carrier 30gh.discharhe and liquid line pressure difference is 30 psig. My question is to calculate the condenser TD, subtract the air temperature from discharge head pressure or liquid line pressure?
    From discharge head pressure, before the heat exchange takes place.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    417
    Rep Power
    22

    Re: how to calculate actual air cooled condenser TD.

    Quote Originally Posted by marc5180 View Post
    From discharge head pressure, before the heat exchange takes place.
    In microprocessor based control chiller system, the discharge saturation sensor fixed on the centre of condenser or transducer fixed on discharge service valve, it is not consider the liquid line pressure. As beeran said, if there is 30 psig high side pressure drops, raising a question, which pressure will be considered as saturation temp and measuring TD.

  8. #8
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: how to calculate actual air cooled condenser TD.

    Use discharge head pressure.............since due to pressure losses in condenser / piping , liquid pressure could be shade lower