22-02-2006, 11:16 AM #1
Help with college homework, Please.
How would you dehydrate a 20kw water cooled package unit flooded internally.
my answer
After recovering all of the contaminated refrigerant, I would then pressure test with Oxygen free Nitrogen. Then triple vacuum test the system, leaving it for 12 hours on the third vacuum. I would then release the vacuum, replace the filter dryer, then vacuum test again, the recover new refrigerant.
Plese comment. Have I missed something.
-
22-02-2006, 11:30 AM #2
Re: Help with college homework, Please.
yes you have. you would need to change the oil. also its not just a case of vacuum for 12 hours, it needs to be drawn down to an acceptable level.
Last edited by slingblade; 22-02-2006 at 11:33 AM.
Takes a licking, keeps on ticking.
-
22-02-2006, 11:34 AM #3
Re: Help with college homework, Please.
Change the oil in the compressure ? and draw it down to 20mbar
-
22-02-2006, 11:38 AM #4
Re: Help with college homework, Please.
How would you dehydrate a 20kw water cooled package unit flooded internally.
my answer
After recovering all of the contaminated refrigerant
I would then pressure test with Oxygen free Nitrogen.
Then triple vacuum test the system, leaving it for 12 hours on the third vacuum.
You can then verify that all the moisture is out of the system by applying a vacuum. If you fail to achieve a good vacuum that holds a steady gauge reading with the circuit isolated then you probably still have moisture present. Use a good drier before your vac pump.
I would then release the vacuum, replace the filter dryer,
the recover new refrigerant.
-
22-02-2006, 11:46 AM #5
Re: Help with college homework, Please.
if i was called to a burst chiller:-
1. find hole. 9/10 burst evap.
2. recover any gas.
3. remove as much water as possible by blowing with ofn (this may involve breaking open components cond. oil sep. etc)
4. repair hole (new evap.)
5. drian comp oil and remove drier.
6. pressure test
7. evac to say 50 micron (system size dependant) break with ofn.
8. new oil and drier.
9. evac. as before.
10. charge and commission.
11. very large invoice.
12 pub.
hope this helps.Takes a licking, keeps on ticking.
-
22-02-2006, 01:16 PM #6
Re: Help with college homework, Please.
Cool thanks for that,
-
22-02-2006, 02:22 PM #7
Re: Help with college homework, Please.
Thanks the quesion fr my homework was "How would you dehydrate a 20kw water cooled package unit flooded internally"
So my answer would be
Find when it has caused the flood and make suitable repairs. Open system and leave if possible open in a heated area to allow mositure to evporate, then blow system with ofn, drian comp oil and remove drier.
,pressure test evac to 50 micron break with ofn.
new oil and drier. evac. as before. charge and commission.
Does these seem ok
-
22-02-2006, 03:24 PM #8
Re: Help with college homework, Please.
Better answer but if you want top marks you ought to elaborate a bit on each task, explaining why you need to carry out the tasks i.e. - how to determine if all the moisture has gone.
Also, it would be good practice to change the TEV as this would most probably contaminated internally. What about fitting a moisture indicator?
Think outside of the box
-
22-02-2006, 03:42 PM #9
Re: Help with college homework, Please.
Also, it would be good practice to change the TEV as this would most probably contaminated internally.Takes a licking, keeps on ticking.
-
Re: Help with college homework, Please.
Originally Posted by slingblade
Corrosion from being submerged if it's a sea water cooler, or dirt if it's freshwater.
if he's allready facing a large bill, why save $40 by not changing a part, when it might cost him another pretty penny to have an engineer come out to do the job a few days later
Also, remove the filter drier before vacuuming... why leave a filter saturated in water... it'll only take longer to dry out the plant.-Cheers-
Tycho
-
22-02-2006, 04:25 PM #11
Re: Help with college homework, Please.
Corrosion from being submerged if it's a sea water cooler, or dirt if it's freshwater.Takes a licking, keeps on ticking.
-
Re: Help with college homework, Please.
Originally Posted by slingblade
well, ok, maybe not replace, lets call it inspect and test.
The Tev has moving parts, is located in connection with both the chiller and condenser, and in case of a leak in either of those two large enough to get water into the system the tev will be effected.
Of course if the system was completely flooded with water (I've had those) I would remove and service all valves, inspect the compressor for damage and if necessary serviced it (combine accident with xxxx hour service).
usually something like a complete waterflood of a plant will be noticed in short time so internal corrosion on the chiller tube shell and condenser (wall thickness of 15-25mm, special alloy in the tubes) will be minimal once you have dried out the plant and recharged *****, no oxygen, no corrosion.
********edit********
I don't know about you, but I'm in this job to make money for my company so they can pay me
I will not lie to a customer to make more money, I will tell him what I think is best and then it's up to him to consult others or let me do what I think is best.
in the end, I'm gonna be the one to blame (in his eyes) if his plant isnt as good (or better ) as it was before the accident.Last edited by Tycho; 22-02-2006 at 06:53 PM.
-Cheers-
Tycho
-
22-02-2006, 08:35 PM #13
Re: Help with college homework, Please.
Hi
Nobody has recommended heating the evaporator to aid moisture removal. Add heat anywhere you can, compressor, receiver, evaporator and condenser. Only realy way to remove the moisture.
Don't forget the compressor oil, drain it prior to vaccuming and add some after the main vac, giving it a quick vac after adding the new oil. Don't add the oil before the moisture has been removed.
Kind Regards. Andy
-
22-02-2006, 08:38 PM #14
Re: Help with college homework, Please.
Nobody has recommended heating the evaporator to aid moisture removal.
I would recommend that you leave the system open in a hot area, i.e. in front of a warm air heater or if this is not possible then apply heat to the unit possibly with a portable propane blower (floor standing room heater type).
-
22-02-2006, 08:42 PM #15
Re: Help with college homework, Please.
Originally Posted by Tycho
-
22-02-2006, 09:58 PM #16
Re: Help with college homework, Please.
Come on Andy That was my first reply
Don't forget the compressor oil, drain it prior to vaccuming and add some after the main vac, giving it a quick vac after adding the new oil. Don't add the oil before the moisture has been removed.Takes a licking, keeps on ticking.
-
22-02-2006, 10:07 PM #17
Re: Help with college homework, Please.
Originally Posted by slingblade
-
22-02-2006, 10:12 PM #18
Re: Help with college homework, Please.
Originally Posted by frank
Never thought of leaving it open whilst heating
I usually use an old vacumn pump for the early stage, changing the oil regularly (when it goes emulified), braeking the vac often with OFN. When the vacumn stops dropping I then bring out the new pump to finish the job off
Kind Regards. Andy