    Condenser THR on Economized Screw Package



    Hello,

    I can't seem to remember whether the condenser THR is based on the BHP and Refrigeration TR only in the case of an economized screw. Do I need to account for the economizer load and oil cooling load in the condenser THR as well? i.e I have 280 BHP/80 TR Capacity, plus 30 TR Economizer and 20 TR Oil cooling. Total THR is?

    Thanks,

    RE



  2. #2
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Condenser THR on Economized Screw Package

    All these loads go to the condenser.

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Condenser THR on Economized Screw Package

    Hi, RefrigEng1

    Quote Originally Posted by RefrigEng1 View Post
    Hello,

    I can't seem to remember whether the condenser THR is based on the BHP and Refrigeration TR only in the case of an economized screw. Do I need to account for the economizer load and oil cooling load in the condenser THR as well? i.e I have 280 BHP/80 TR Capacity, plus 30 TR Economizer and 20 TR Oil cooling. Total THR is?

    Thanks,

    RE
    you need to calculate condenser for all loads like ... power of electrical motor, refrigeration load, economizer load, oil cooling load in case of refrigerant oil cooler ... it is the only way to reject total heat back to the mother nature .... of course with some addition in capacity due to fouling factor ...

    of course if you have water oil cooler it is not added to condenser capacity ...

    read this, please

    http://www.achrnews.com/articles/siz...ive-condensers

    http://www.achrnews.com/articles/120127

    http://library.kfupm.edu.sa/ISI/2006/4-2006.pdf

    http://lms.i-know.com/pluginfile.php...%20Control.pdf

    https://www.ideals.illinois.edu/bits...9750/TR048.pdf


    Hope this is of some help to you ..

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Condenser THR on Economized Screw Package

    If oil cooling water have separate water tank and cooling tower, oil cooling load should not be included. If common water tank used for oil cooling and for evaporative condensers, oil cooling load should be included.