Thread: DT of water heat excanger
-
26-02-2006, 11:57 AM #1
DT of water heat excanger
Why all chiller manufacturer vants 5 to 7 C DT.Would it be so bad to have 2 to 3 C DT?
Q = m c DT in boath case.When changing DT ,m rises so Q is the same.I know I miss something can some of you open my eyes.
Best regards,
Renato
-
26-02-2006, 12:09 PM #2
Re: DT of water heat excanger
Renato
Larger td means a smaller evaporator, cheaper solution.
The dt you are refering to is the difference between the fluid on and off the chiller temperature. This relates to the design of the air side heat exchanger (air handling unit) or the process side heat exchanger. Most designs refer to a 6 to 10 td on the airside, again to keep the coil size down and the cost of the airside haet exchanger.
Kind Regards. Andy
-
26-02-2006, 02:05 PM #3
Re: DT of water heat excanger
Renato,
As Andy said, if you go down on dt, the 'm' - flow rate of liquid through the evaporator - increases, hence the bigger evaporator size. But this means also a bigger evaporator pump, increasing your investment/initial cost. Now, with a bigger pump your running cost will be also higher.
So, you lose on both initial and running cost.
Similar Threads
-
cold river water
By eftimios in forum FundamentalsReplies: 8Last Post: 09-11-2008, 06:37 PM -
Refrigerant to water heat exchangers
By sunwind in forum Technical DiscussionsReplies: 20Last Post: 24-06-2008, 01:40 PM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
VFD heat pump water heater?
By star882 in forum New TechnologiesReplies: 0Last Post: 23-05-2006, 08:36 PM -
Mcquay water source heat pump
By bernie in forum Air ConditioningReplies: 2Last Post: 10-02-2003, 01:53 AM