    Angry Pipes freezing up and evaporator over condensating



    Hi,

    I have a split system with condenser outside at floor level about 3metres below evaporator.
    In a really humid testing lab.
    I cleaned the totally blocked filter in the evaporator, tested the LP to be 4bar (410a) no means of testing HP.

    The pipes still freeze up from outside the condensor right into the evaporator and the condensation runs like a snotty school kids nose.

    Any ideas.



  2. #2
    Join Date
    Jan 2009
    Location
    Canary Islands
    Age
    74
    Posts
    144
    Rep Power
    16

    Re: Pipes freezing up and evaporator over condensating

    Suction pressure is, as you know, dependent on variables. Air over condenser for one.
    Generally speaking, with most small split systems, the expansion device is a capillary within the exterior unit and if the liquid line is frosting, the system has a leak and has therefore lost refrigerant. As the system contains R410a, this is borne out by the SP being only 4b. We here in Tenerife expect to see 8 to 10b on a fully charged, no problem system! In UK, maybe 7 to 9b.
    Again, most small splits only have an access port on the suction valve.
    The correct procedure for recovery, leak test and repair, evacuation and recharge must be carried out.
    Graham
    en boca cerrada no entran moscas

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Pipes freezing up and evaporator over condensating

    Lack of refrigerant, you need to recover all of it, find the leak with OFN, repair it and charge with virgin 410 refrigerant,

  4. #4
    Join Date
    Apr 2013
    Location
    ENGLAND
    Posts
    10
    Rep Power
    0

    Re: Pipes freezing up and evaporator over condensating

    Hi,

    The evaporator was incredibly dirty, so i cleaned this out, i have been advised to check that the fan is spinning freely in the evaportator. If the fan is OK, then it is time to find the leak.

    Thanks guys....nice one

  5. #5
    Join Date
    Feb 2008
    Location
    sydney
    Age
    52
    Posts
    32
    Rep Power
    0

    Re: Pipes freezing up and evaporator over condensating

    needs gas fix the leak